Site Supply
Y
YTSOxford
Hi all,
my builder who I work for is demolishing a house at the moment and is wanting me to put in a temp supply for chargers etc. Any ideas what set up I should have here?
Also I have read you can't have a pme supply - why is this and would a rod get over this?
Thanks!
Just knock up a simple site board with a 2 way Cu - 40A 30mA RCD and a 20A MCB, feeding a couple of twin sockets.
If the house is being totally demolished will you not need a geney???
704.411.3.1
"A TNCS system shall not be used for the supply to a construction site,except for the supply to a fixed building of the construction site"...........you will need to factor that in to any arrangements for a temporary supply.
YTSOxford,
Deleted member 9648,