C

cobrauk

I have not install site temps for a while so cant find in writing what i think is correct so please help if you can, as I need to have this info to insert into my test certificate.

I am sure that I remember reading somewhere that the site containers offices etc are not glassed as temporary as they do not move around and have fixed wiring from the supply so do not need to be checked every 3 months as lay down in the recommended testing periods for construction sites installations and the 3 month retest time only applies to circuits installed within the new building area IE (temporary sockets, lights, transformer, etc).

Am I correct in thinking this please ?
 
This always seems to be a unknown. All the retest times that are written are guides only as far as I know. The regs do say it is the installers decision on there knowledge of the installation to determine a suitable re-test period. Any written times from any books are only supposed to be there to guide your decision.
 
A lot of sites require testing 3monthly to satisfy their own H&S bods. Also insist on tools etc to be PAT 3monthly.
should say that this is for everything on site , cabins offices the lot.
 
After the initial EIC cert is issued after the set up. Which cert is to be used for the 3 monthly testing?
EICR, like any other periodical.
The aim is to find out if any faults have developed in the interim time period.

I’m sure the OPs case, it’s been tested a number of times in the 9 years since it was first posted
 

Reply to Site temporary re-testing time period question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
686

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top