Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size with this 16mm or 10mm ? Thanks
 
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size with this 16mm or 10mm ? Thanks
If you are referring to the typical UK insulated and sheathed singles used as meter tails these don't include a protective conductor in the cable. The norm would be to run a 16mm^2 Earthing conductor alongside.
 
If you are referring to the typical UK insulated and sheathed singles used as meter tails these don't include a protective conductor in the cable. The norm would be to run a 16mm^2 Earthing conductor alongside.
ye if it was a 100 amp main fuse i would install 25mm double insulated tails with a 16mm earth, so if it is an 80 amp fuse then i know i can use 16mm double insulated tails but is a 10mm earth sufficient or does it have to be a 16mm?
 
ye if it was a 100 amp main fuse i would install 25mm double insulated tails with a 16mm earth, so if it is an 80 amp fuse then i know i can use 16mm double insulated tails but is a 10mm earth sufficient or does it have to be a 16mm?
If selected (as opposed to calculated) then 16mm^2 is required. As I stated, 16mm^2 is the norm.
 
ye if it was a 100 amp main fuse i would install 25mm double insulated tails with a 16mm earth, so if it is an 80 amp fuse then i know i can use 16mm double insulated tails but is a 10mm earth sufficient or does it have to be a 16mm?

This depends on a number of factors.

If you are using the table 54.7 method then it will need to be 16mm.

If, however, you are calculating the size required then you may find that 6mm (or less) satisfies the adiabatic equation. But you also need to consider the earthing system as this will affect the size that the earthing conductor needs to be to satisfy bonding requirements.
 

Reply to size of earth on 16mm mains tails in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
521
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top