I have a well pump and motor on it's own meter. I do not have the specs on the motor. It pulls up from about 60' down, at about 45 gpm. And my bill is for about 800 kWh per month. The coop utility power goes out periodically and we want to have a propane generator that I can use to keep my water available and a small milk house heater on when the power goes out. I'm not sure what size to buy. How many watt generator do you think I should buy? Thank you.
 
The generator and utility feed breaker must be interlocked to meet code. Otherwise by mistake you could feed generator power back into the utility line and electrocute the guy working in the hole in the road. For the generator sizing, you really should try to get some specs on the pump or measure the current.
Thank you. I don't know how to do that.

I'm not above paying an electrician but I can't seem to find one.
I have to agree with @Lucien that you need a interlock kit or transfer switch because it can be very dangerous if you get confused. Well pumps doesn’t have a starter nor heaters, it’s just a set of contacts that pull in when the pressure switch drops to its desired setting. 45 gallons per minute is a lot of water and you Need to set your pressure switch a little lower which is probably why your motor keeps going out. I’ve had mine 23 years and changed the motor 1 time
 
I have to agree with @Lucien that you need a interlock kit or transfer switch because it can be very dangerous if you get confused. Well pumps doesn’t have a starter nor heaters, it’s just a set of contacts that pull in when the pressure switch drops to its desired setting. 45 gallons per minute is a lot of water and you Need to set your pressure switch a little lower which is probably why your motor keeps going out. I’ve had mine 23 years and changed the motor 1 time
I think I'm still at 35 gpm (even though my water right is 45 gpm). I have/had things set at 40 psi on, and 60 psi off. But I also have a cycle stop valve in the line. Some well people have set that out of the range on the directions in order to give me more pressure due to friction loss far from the well. But I've set it back in range, per the directions, because I seem to have plenty of pressure 2,000 feet away.
 
I think I'm still at 35 gpm (even though my water right is 45 gpm). I have/had things set at 40 psi on, and 60 psi off. But I also have a cycle stop valve in the line. Some well people have set that out of the range on the directions in order to give me more pressure due to friction loss far from the well. But I've set it back in range, per the directions, because I seem to have plenty of pressure 2,000 feet away.
My friends well pumps 27 gallons a minute and they told him that they could supply a whole neighborhood
 

Reply to Sizing a propane standby generator in the USA Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician Laws and Regulations related to Electrics and Electricals within the United Kingdom. Electrician talk, questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top