Indeed.
Even 4mm is fine on a 32, but lets not go there.
I went there Jason 6mm on a 40, Somebody prove me wrong ??
So should we forget about the BRB and just do what we feel like? Because we know better? I know its not law but the book is there for a reason.
To me one reg is as important as another, esp if giving advice.
Pease read 433.1.1
I was not questioning this, but how will putting a 32A protective device on a cct that has a 40A load meet co-ordination?
Am i missing someting?
The electrician should use his experiance and judgement when assessing the maximum demand of a circuit.
The loading of a cooker as advised by the manufacturer is simply the sum of all elements in the cooker.
This includes the grill which is not on when the oven is on.
Unlike an electric shower(which is either fully on or off), the cooker is never fully on and I think it not unreasonable to assess the load as below that which the manufactuere states.