So should we forget about the BRB and just do what we feel like? Because we know better? I know its not law but the book is there for a reason.

To me one reg is as important as another, esp if giving advice.

Pease read 433.1.1

Dont forget that most of us are experienced electricians and are capable of a bit of engineering judgement and common sense
 
Last edited:
The first 10A of the rated current plus 30% of the remainder of the rated current in excess of 10A plus 5A if a socket-outlet is incorporated in the cooker control unit. (Well it helps things along bit diverse though):)
 
I was not questioning this, but how will putting a 32A protective device on a cct that has a 40A load meet co-ordination?

Am i missing someting?

The electrician should use his experiance and judgement when assessing the maximum demand of a circuit.

The loading of a cooker as advised by the manufacturer is simply the sum of all elements in the cooker.
This includes the grill which is not on when the oven is on.

Unlike an electric shower(which is either fully on or off), the cooker is never fully on and I think it not unreasonable to assess the load as below that which the manufactuere states.
 
The electrician should use his experiance and judgement when assessing the maximum demand of a circuit.

The loading of a cooker as advised by the manufacturer is simply the sum of all elements in the cooker.
This includes the grill which is not on when the oven is on.

Unlike an electric shower(which is either fully on or off), the cooker is never fully on and I think it not unreasonable to assess the load as below that which the manufactuere states.

All the above Andy along with diversity factors for cooking appliances as per my last post,cannot see where there is a problem really can't :)
 

Reply to Sizing Cooker fuse / diversity...confused in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
1K
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
563

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top