3% on Dc in guide? 1% AC
OK. Let’s try to get a consensus here.
From the DTI guide:
2.1.2: Use (total) Voc and Isc to specify ‘components’, ie switches, connectors, cable type, etc, using safety factors of 15% for voltage, and 25% for current.
2.1.4.1 Cable sizing: Apply the safety factors as above (plus any BS 7671 derating). It’s not specified which parameters to use for the calculations though, which I think it should.
As Screwdriver says in his excellent post #5, Imp and Vmp are used here.
I hold the DTI guide is wrong not to state this clearly.
2.1.4.1 also states, clearly, that the Voltage Drop between array and inverter should be less than 3% (one tick therefore a recommendation.) So working on a 2.99 % drop for your dc calculations is fine.
2.1.6 is titled ‘Main d.c. cable’ but is actually (I think) talking about panel interconnects and other local array wiring, which is confusing. Using, again Voc and Isc, it applies only to cable type; it’s nothing to do with cable sizing per se. This is where I went wrong in the beginning.
Does anyone have a referenced formula, in metres and mm[SUP]2[/SUP] (not, like most on the web, AWG & feet) for DC volt drop calcs in underground SWA please?
the volt drop is negligible particularly on this system because the voltage is so much higher than standard AC runs.
but on this system the voltage in operation will be somewhere between 350-400V, and most of the systems we design are in this range as this is the peak operating range of the inverters we use (and most inverters on the market).I've often seen this repeated in this forum but it depends totally on the array design.
Many 230 - 250W panels have 60 cells and so a Vmpp in the region of 30V. A 4kw array divided into 2 strings of 8 will therefore have string voltages of 240V and (neglecting skin effect losses on AC) for the same cross-section the AC and DC losses per m of cable will be much the same.
but on this system the voltage in operation will be somewhere between 350-400V.
... Maybe someone should do the definitive calculation using all the right figures to put us out of our misery.
I don't think this is quite right, 12.35A is for both strings (are you connecting them in parallel at source and if so why the four-core cable?), and also includes the 1.25 safety margin which you don't need when calculating voltage drop at Impp. This will put the volt drop down by at least 20% and possibly a further factor of two.Here you are, now I understand which figure is which (NO thanks to the DTI guide, but many thanks to others on this forum) it’s easy:
Total current at max power, where panel Imp = 4.94A, 4.94 x 2 x 1.25 = 12.35A
Total voltage at max power, where panel Vmp = 50.6V, 50.6V x 8 x 1.15 = 466V
Total Isc where panel Isc = 5.35A, 5.35 x 2 x 1.25 = 13.4A
Total Voc where panel Voc = 60.5V, 60.5 x 8 x 1.15 = 560V
Cable volt drop calculation for the 165m DC run (now measured accurately) on 10mm 4-core (4.7 mA/V/m) is:
Vd = 4.7 x 165 x 12.35 / 1000 v = 9.58V
Again, the 466V includes a 1.15 safety margin, removing this will put the actual % volt drop up by 15%.9.58/466 x 100% = 2.06%
I don't think this is quite right, 12.35A is for both strings (are you connecting them in parallel at source and if so why the four-core cable?), and also includes the 1.25 safety margin which you don't need when calculating voltage drop at Impp. This will put the volt drop down by at least 20% and possibly a further factor of two.
Again, the 466V includes a 1.15 safety margin, removing this will put the actual % volt drop up by 15%.
OK, understood. So is this (finally!) right?:
Vd = 4.7 x 165 x (4.94 x 2) / 1000 v = 7.66V
7.66/(50.6V x 8)x 100% = 1.89%
ah right, I did look, but missed that bit.Sorry, I was thrown off the scent by screwdriver's assumption of 30V per panel.
But I don't think you would get away with 4mm^2 in this instance because as the OP says it is a 150m run (so it is "in a field" to quote your earlier posting).
Maybe someone should do the definitive calculation using all the right figures to put us out of our misery.
Reply to the thread, titled "Sizing DC cables, PV Array to Inverter. Confused. Help please!" which is posted in Solar PV Forum | Solar Panels Forum on Electricians Forums.