Hi, am looking to upgrade my electrical shower from 9.5 to 10.5kw and am unsure if my cable is upto the job as its 6mm attached to a 40A fuse. The length of the run from fusebox to shower is approx 12-15m so I am trying to check if its a viable project as I have no desire to upgrade the cable to 10mm given the route.
If there is a formula for this calculation then that would be a big help.
Thanks
 
What do the manufacturers instructions say? I would expect they would say 10mm cable as 10.5kW (45.6Amps) and the instructions would/should override any calculations.

I really depends on how the cable is installed - for example from the IET Wiring Regulations, if run in insulated stud wall its current carrying capacity (CCC) could be as low as 27.5A . Enclosed in a plastered wall - 32A so you see way below what a 10.5kW shower would draw.
 
Careful when swapping out shower heaters of this capacity on 40a devices, check the voltage at the shower terminals.

A 9.5kW 240v heater will draw 39.5a.
A 9.5kW 230v heater will draw 41.3a

But.

A 9.5kW 230v heater connected to a 240v supply will draw 43a, and is in fact operating as a 10.3kW heater.

Usually it seems to pass unnoticed as most people take 5-10 minute showers and the 40a device will tolerate that on its slow-to-act thermal overload, but occasionally you'll get a plumber wapping' in a "like4like" and get confused when it trips. the safer option is go for a 9kW, which in the above over- volts scenario is still 9.8kW/41a
 

Reply to the thread, titled "Sizing of a cable for a shower." which is posted in DIY Electrical Advice on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwick
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Sizing of a cable for a shower.
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
4

Thread Tags

Tags Tags
None

Thread statistics

Created
haf1963,
Last reply from
Teddy Lop,
Replies
4
Views
101
Back
Top