Slightly high ZS reading | on ElectriciansForums

Discuss Slightly high ZS reading in the Australia area at ElectriciansForums.net

A

andyww

Hi

Have installed a new ring circuit - for a kitchen - lots of points (19 in total) - TNS earthing, max ZS should be 1.16 - I'm getting 1.41 - have checked tightness of all terminations and all are good

anyone got any ideas?

Cheers
 
Hi

Have installed a new ring circuit - for a kitchen - lots of points (19 in total) - TNS earthing, max ZS should be 1.16 - I'm getting 1.41 - have checked tightness of all terminations and all are good

anyone got any ideas?

Cheers

cable length.should have split into two rings. zs=ze+r1+r2.table 9a on site guide
 
But the circuit still has to comply
The Zs reading then multiplied by 1.2 will be 1.73

Lower the breaker rating
Split the ring into 20 amp radials
Install supplementary bonding but,
probably re test with another meter,just to be sure before butchering :)
 
Thats the reason why Zs should not be calculated.

New sockets can also give strange readings due to contacts inside.

Try pushing the plug on your tester in and out a few times to 'clean' the contacts.
 
Thats the reason why Zs should not be calculated.

New sockets can also give strange readings due to contacts inside.

Try pushing the plug on your tester in and out a few times to 'clean' the contacts.

Put an extra socket at me mums for a minor on NIC assessment but couldnt do Zs as kt61 hasnt got no trip function and alto al4588 loop isnt cal'd so done Ze and got 6.2ohms lol phoned me old m8 at SSE and within 45mins a guy was there and now got PME with Ze of 0.13ohms :) The CU was changed about 5yrs ago by a supposed sparks when me dad was alive but no tests/certs etc :mad: even used a bs951 on supply for earth & that was loose ! wasnt even touching anything but tape !
Dont know why we bother ! im sick of finding shoddy work he had even put a socket in the frt rm with NO cpc :rolleyes: !
 
Last edited by a moderator:

Reply to Slightly high ZS reading in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
600
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top