andyww

Hi

Have installed a new ring circuit - for a kitchen - lots of points (19 in total) - TNS earthing, max ZS should be 1.16 - I'm getting 1.41 - have checked tightness of all terminations and all are good

anyone got any ideas?

Cheers
 
Hi

Have installed a new ring circuit - for a kitchen - lots of points (19 in total) - TNS earthing, max ZS should be 1.16 - I'm getting 1.41 - have checked tightness of all terminations and all are good

anyone got any ideas?

Cheers

Personelly would have installed more then 1 ring, what the total Kw that expected to connected to the ring, would have installed possible two or three ring or radial for washing machine, dryer etc is applicable.

[SIZE=2 said:
andyww[/SIZE];61865]Hi

Have installed a new ring circuit - for a kitchen - lots of points (19 in total) - TNS earthing, max ZS should be 1.16 - I'm getting 1.41 - have checked tightness of all terminations and all are good

anyone got any ideas?

Cheers

Andyww when you did the test was your meter on the Zs 15 mA setting (limited current type) that the reason for the high reading and the difference between Ze + (R1+R2) values measured.

 
Last edited by a moderator:

Reply to Slightly high ZS reading in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

Yes, probably overthinkig, thanks.
Replies
6
Views
812
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top