sedgy34

got an sma 4000tl20 doing a 4kw, set at G59 need to change it to G83 "high grid voltage"ive had permission from DNO how do i do this without calling sma (as they are closed) for the weekend
got bluetooth device connected etc
 
you need a grid guard code, then IIRC it's in setting >> AC or settings >> grid monitoring

something like that anyway
 
email or call sma for a grid guard code once they give it to you change the setting on the sunny boy via bluetooth from sunny explorer
 