Precisely Bruce.
High-resistance, "slow burning" DC leakage currents may be generated by a DC cable insulation rubbing on metalwork, for example, or from excessive moisture/dew especially in early mornings. (On a non-bonded/floating system...).
I've said before that I'm no expert on general wiring reg's etc but what I will add also is that if there are any buried cables (that are not armoured), then an RCD fitted should be 30mA rated, right? Most TL inverter manufacturers will tell you what their leakage current values are but I suspect that nuisance tripping would be a problem in most regards for 30mA RCDs. If TL inverters are an absolute must to be used then it could be said that all possible efforts should be made to "dial-out" any install methods that result in the requirement of a 30mA RCD.
One good idea would be to get to know your inverter manufacturers and their spec's well. They don't typically give out leakage current details (amplitude or harmonics/frequency info) on their standard spec sheets but when asked what trip limit RCD to fit, they should be able to advise based on their own knowledge of their product's leakage current characteristics. The least they should do is provide the info you need to make the decision. For TL inverters, your MCS inspector may also provide you with some guidance as to what would be accepted or not. Under the terms of the current guidelines, it could be inferred that ALL transformer-less inverter installations should be fitted with a Type B RCD, regardless of what the manufacturer says.
Hope this helps. At the end of the day, we (Sibert) can't dictate what type and rating of RCD should be fitted. With Doepke's assistance we can only support what the regulations state. However, with additional technical information provided by the inverter manufacturer, and the design/installation engineer's expertise and experience with the standards/regulations and installation environment, we can certainly help to find the best solution.
As a guide for anyone who is curious, a 16A, 100mA, 2-pole Type A RCD should cost around ÂŁ45ea. A 16A, 100mA, 2-pole Type B RCD should cost between ÂŁ300 and ÂŁ350 (depending what model type needed/selected)