OP
1billy wiz
what about the isolation??can you feed it straight in or does it need a switch to isolate for maintenance?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
what about the isolation??
Just highlighting some differences between 7671 & building regs.
From BS 7671
Fire detection circuits must be supplied independently of other circuits and not protected by an Rcd protecting multiple circuits. 560.7.1
From Building regs.
The smoke alarms have to be interconnected, have a battery backup, and be permanently supplied from a separate way in the ccu, or supplied from a local lighting circuit that is regularly used. Please note this requirement conflicts with 560.7.1
Except for TT systems, the circuit supplying a smoke alarm should not be protected by an RCD. For TT systems the smoke alarm must be supplied from the fixed equipment section of the ccu, not through a 30mA RCD.
560.7.1 Circuits of safety services shall be independent of other circuits.
NOTE: This means that any electrical fault, maintenance or modification work on one system must not affect the correct functioning of the other. This may necessitate seperation by fire-resistant materials or different routes or enclosures.
Where does it mention RCDs???
I REGRET becoming an electrician, it's so fickle & at times my confidence is shot to bit's
Reply to Smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net