Hi everyone,

I’m installing two smoke alarms and a heat alarm in a standard two-bedroom renovation. I was considering omitting RCBO protection for the smoke/heat circuits since they’re part of a safety system. Does that approach sound correct, or would it be better to integrate them into the lighting circuit instead?

Appreciate any advice!
 
It's fine doing that provided the RCD isn't required for additional or fault protection.
 
although it may be fine doing that, i prefer to have them on the lighting circuit.

after all, if they are separate and the breaker trips, eventually when the batteries fail they will be off and nobody will notice / care.
 
I think most modern detectors beep if there’s a powercut…. Or have a “power” light … So you should know if the breaker tripped.
 
although it may be fine doing that, i prefer to have them on the lighting circuit.

after all, if they are separate and the breaker trips, eventually when the batteries fail they will be off and nobody will notice / care.
Thanks all!

So it’s okay to put smokes on a RCBO circuit? I was taught to mitigate the RCD protection on safety circuits
 
If it is installed in such a manner and ADS is satisfied without an RCD it doesn't need one but putting it on an RCD is also fine.
 
If it is installed in such a manner and ADS is satisfied without an RCD it doesn't need one but putting it on an RCD is also fine.
Okay so it’s a PME system so ADS could be met via the 6Amp Breaker!

Removing the RCD would mean chasing the cable deeper etc! So if it can go on an RCBO circuit then it’ll go on one! It does make sense to combine it with lights as then it’ll always be switched on 😄
 
Lights would be on rcd protection now if you were to minor works on that circuit.

The only thing that might dictate rcd for smokes is buried less than 50mm… unlikely you are going into a wall.
Or are you putting one on a bathroom? Also unlikely.


Is mains detectors called for, or could you fit the aico 10 year battery type with the radio interlink?

No redecoration required. Whole house fitted in an hour.
 
If you make it easy for a domestic customer to disable smoke alarms, then they will, so definitely in with an important lighting circuit.
It's a property renovation, redecoration doesn't need to be considered, so hard wired is preferable.
They'll have battery back up, so the "safety system" not RCD protected is irrelevant.
 
I generally wire as a separate feed from a lighting circuit breaker. Figure it makes any testing or potential fault finding easier.

But yeah the "They" like smokes on circuits to which "power loss will be observed". And TBF some people seem remarkably resilient to the chirps of failing smokes, which seems incredible for someone who's a bit spesh with sensory input. Mind you, the "They" also require non-tamper battery backup (that's yer cheapskate 9v instead of recharging) but nobody seems to give a ---- about that do they...
 
I generally wire as a separate feed from a lighting circuit breaker. Figure it makes any testing or potential fault finding easier.

But yeah the "They" like smokes on circuits to which "power loss will be observed". And TBF some people seem remarkably resilient to the chirps of failing smokes, which seems incredible for someone who's a bit spesh with sensory input. Mind you, the "They" also require non-tamper battery backup (that's yer cheapskate 9v instead of recharging) but nobody seems to give a ---- about that do they...
Really really great advise! It will always be wired into the lighting at the breaker but it’s good to refresh! By that I mean ran back to the board not just taking from a switch or ceiling rose!

It’s settled the smokes will go on the downstairs lighting RCBO!

Thanks as always electrical over lords! 🙏
 

Reply to the thread, titled "Smokes & Heat separate circuit to lighting?" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

LmarshallSparks

Supporter
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marshall’s Co.

Thread Information

Title
Smokes & Heat separate circuit to lighting?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
LmarshallSparks,
Last reply from
LmarshallSparks,
Replies
11
Views
191

Advert

Back
Top