sheephat
-
I posted this up on yahoo answers but I figure you guys are probably more qualified to answer my question
I have a generator in the building I am working on. It appears quite dated, but its stats are as follows: it’s a 415 Volt 3 Phase Diesel Generator.
On the plate of the generator:
415V
3 Phase
640KVA
520KW
Power Factor 0.8
902 Amps
So my question is:
We are testing the generator to its full load, now my load is at power factor 1. Would I be correct in assuming that because my load is power factor 1 that the full load of my generator is 640kW not 520kW.
Or is it that my actual power loading is rated at 520kW, but that load is allowed to be inductive or capacitive to 0.8.
Because it says 900 amps on the plate I am therefore under the assumption that regardless of my load characteristics, as long as I do not exceed 900 amps there should be no problem. Or is it a case that my load can only be 520kW and the highest I can allow the phase to go out is up to 640kVA.
Hope that makes sense, ill edit if not. Thanks for reading.
I have a generator in the building I am working on. It appears quite dated, but its stats are as follows: it’s a 415 Volt 3 Phase Diesel Generator.
On the plate of the generator:
415V
3 Phase
640KVA
520KW
Power Factor 0.8
902 Amps
So my question is:
We are testing the generator to its full load, now my load is at power factor 1. Would I be correct in assuming that because my load is power factor 1 that the full load of my generator is 640kW not 520kW.
Or is it that my actual power loading is rated at 520kW, but that load is allowed to be inductive or capacitive to 0.8.
Because it says 900 amps on the plate I am therefore under the assumption that regardless of my load characteristics, as long as I do not exceed 900 amps there should be no problem. Or is it a case that my load can only be 520kW and the highest I can allow the phase to go out is up to 640kVA.
Hope that makes sense, ill edit if not. Thanks for reading.