I can’t understand this argument.
640KVA 415V @ unity PF = 890A
520KVA 415V @ 0.8 PF = 868A
As near as damn it 900A
 
The altitude and the ambient tempurature must surely be irrelevant how can it affect the generator rating that much, beside lets pretend we have ideal conditions.

@Rockingit - I wanted to turn the load bank up and take over the whole testing process but they wouldnt let me lol.
 
640 kva @ 80% pf = 520 kw, actual usable power.
but I like the duel at dawn method with alternator plates. or the rock and roll method :)
 
Last edited:
640 kva @ 80% pf = 520 kw, actual usable power.
but I like the duel at dawn method with alternator plates. or the rock and roll method :)

No-ones trying to dis you...

But i can assure you, that if an alternator has a a current value stated on it's data plate, then that alternator should be expected to be able to provide that current.. You can play with KW and KVA designations all day, but they will both be based on the capability on what the alternators current output has been designed to deliver. As stated previously, the generator will not care a jot what that current is made up from, it will still provide that stated current, ...be it useful current or otherwise.

As for the ambient temperature and altitude, were talking about an in-situ generator installation in a UK City, so the altitude can be ruled out. As for ambient temperature, ...well that is clearly fine going by the test report readings... So let's take it that in this case, both are well within the manufacturers design thresholds, and that no de-rating factors need to be applied.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London - UK

Thread Information

Title
So whats my actual generator rating?
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
sheephat,
Last reply from
Engineer54,
Replies
18
Views
3,364

Advert

Back
Top