What should the magnetic trip value be for a 20amp radial general use circuit?
 
An MCB would be expected to trip instantaneously within one half cycle.
In the UK, our supply has 50 cycles per second (50 Hertz).


Is there a min or max instantaneous trip?

I would imagine that the earth fault loop impedance must be low enough for a none RCD breaker to clear in 0.5/50 of a cycle? Does the same disconnect time also apply to a L+N fault or is it the same for L+PE?
 
It will all depend where on the cycle the fault occurs.
Maximum voltage and current is achieved at each peak.
Shouldn't matter whether the fault is L-E, or L-N.
Current values for instantaneous tripping, can be found in the tables in BS7671.
They are denoted by the straight lines before the line starts to curve in the tables.
 
Is there a min or max instantaneous trip?

I would imagine that the earth fault loop impedance must be low enough for a none RCD breaker to clear in 0.5/50 of a cycle? Does the same disconnect time also apply to a L+N fault or is it the same for L+PE?

Yes, that is the whole point of carrying out Earth fault loop impedance tests.

The same does apply for a L - N fault, the mcb cannot detect what the nature of the fault is, just the magnitude of the current.
 
Id imagine a L-N fault would be less of a hazard to humans in terms of shock, but it sounds like the regs want identical tripping for both L+PE and L+N.


So I guess I am lead to strike a balance between a breaker that has a high enough In trip not to blow on something like a vacuum cleaner starting up, but a low enough In to trip in 0.5/50ths of a cycle assuming a fault on the last socket on the radial since this will have the highest earth fault reading?
 
Id imagine a L-N fault would be less of a hazard to humans in terms of shock, but it sounds like the regs want identical tripping for both L+PE and L+N.


So I guess I am lead to strike a balance between a breaker that has a high enough In trip not to blow on something like a vacuum cleaner starting up, but a low enough In to trip in 0.5/50ths of a cycle assuming a fault on the last socket on the radial since this will have the highest earth fault reading?

What is this question leading up to?
 
What is this question leading up to?

The correct selection of instantaneous trip level for a breaker. The ones that can be ordered come in different trip curves, each with different instantaneous pick up levels. Some are only a few times the handle rating while others go to 12x or more.

If I am looking at it the wrong way let me know :)
 
The correct selection of instantaneous trip level for a breaker. The ones that can be ordered come in different trip curves, each with different instantaneous pick up levels. Some are only a few times the handle rating while others go to 12x or more.

If I am looking at it the wrong way let me know :)

For general use sockets Type B is normally used, the instantaneous trip part is 5X In, these will be adequate for normal loads unless you have something specific in mind that may need a breaker requiring a higher threshold.
 
MCBs whith higher instantaneous trip current values are used, where high start up currents are expected.
For example where there are DOL motors, lots of fluorescent lights, electric heaters, etc.
 

Reply to Socket Breaker in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

T
The gas hob might still need to be plugged in for the ignition, but an electric oven should have its own supply. You may need to employ the...
Replies
4
Views
274
  • Question
I would have to say that something is wrong with the light. I would advise to get an electrician. Good luck
Replies
1
Views
330

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top