An MCB would be expected to trip instantaneously within one half cycle.
In the UK, our supply has 50 cycles per second (50 Hertz).
Is there a min or max instantaneous trip?
I would imagine that the earth fault loop impedance must be low enough for a none RCD breaker to clear in 0.5/50 of a cycle? Does the same disconnect time also apply to a L+N fault or is it the same for L+PE?
It will all depend where on the cycle the fault occurs.
Maximum voltage and current is achieved at each peak.
Shouldn't matter whether the fault is L-E, or L-N.
Current values for instantaneous tripping, can be found in the tables in BS7671.
They are denoted by the straight lines before the line starts to curve in the tables.
Yes, that is the whole point of carrying out Earth fault loop impedance tests.
The same does apply for a L - N fault, the mcb cannot detect what the nature of the fault is, just the magnitude of the current.
Id imagine a L-N fault would be less of a hazard to humans in terms of shock, but it sounds like the regs want identical tripping for both L+PE and L+N.
So I guess I am lead to strike a balance between a breaker that has a high enough In trip not to blow on something like a vacuum cleaner starting up, but a low enough In to trip in 0.5/50ths of a cycle assuming a fault on the last socket on the radial since this will have the highest earth fault reading?
What is this question leading up to?
The correct selection of instantaneous trip level for a breaker. The ones that can be ordered come in different trip curves, each with different instantaneous pick up levels. Some are only a few times the handle rating while others go to 12x or more.
If I am looking at it the wrong way let me know :)
For general use sockets Type B is normally used, the instantaneous trip part is 5X In, these will be adequate for normal loads unless you have something specific in mind that may need a breaker requiring a higher threshold.
MCBs whith higher instantaneous trip current values are used, where high start up currents are expected.
For example where there are DOL motors, lots of fluorescent lights, electric heaters, etc.
Socket Breaker
Gardner,
Gardner,