Don't really think that any extra information is required.
The OP is really just asking what type of MCB should be used for general circuits.
Unfortunately, they've gone about asking the question in a rather round about fashion.
The answer of course being Type B.
I see it in a similar light. My concern is that while a B type will work, certain circuit factors like long runs can increase trip time which would violate code. If I know where to look, or the equations I can compute the values based on known factors and use an EFLI tester to confirm the values.
Wht are you not working to the NEC requirements, overcurrent is dealt with a little differently, maybe explain to us how you provide protection through NEC requirements, im sure many would be interested.
Cheers
Glad you asked. Basically the NEC is more like a shopping list or design guide. If we have X, NEC says reach for Y. If we have A then we pick B, at least the overall structure of the code. Earth fault loop impedance does not exist. For most circuits we just pick a breaker based on the current needed and make sure the wire is sized correctly. Type A, B, C ect breakers do not exist. Most breakers are just 10X to 15X (a few like 15 and 20amp single pole square D breakers are 5 to 6x) the handle rating for instantaneous trip and that works in most cases (basically the equivalent of your highest magnetic trip MCBs but just used everywhere) Larger breakers over 150 or 200 amps generally come with adjustable trip curves for coordination purposes, but few are willing to spend the money for a coordination study so the dials are either left turned down (fault on branch circuit pops the main as well) or are turned all the way up (a fault on a wire means major arc flash/fire cracker time) .
Here is an interesting link on that actually you guys will love LOL:
http://paceforensic.com/pdfs/Circuit_Breakers_The_Myth_of_Safety.pdf
For general use circuits in the USA we use 2.08mm2 wire (14 guage) and 3.31mm2 (12 gauge) protected at 15 and 20amps respectively. No equations exist or higher current ratings like if the wire is clipped directly to a wall.
For the earth wire we just select what article 250 tells us to based on breaker and wire size.
14 gauge, means 14 gauge earth wire
12 gauge, earth wire means 12 gauge earth wire
10 gauge, equals 10 gauge earth wire
8 gauge and 6 gauge, means 10 gauge earth wire
4 gauge means 8 gauge earth wire ect.
Not very technical, but its seen to suffice.
However, in BS7671 my understanding is that earth wires can be smaller than L or N, (such as 2.5mm2 twin with 1.5mm2 earth) but must pass enough current to trip the breaker in 0.5/50 of a cycle. In this regard a difference exists between the NEC and BS7671.