Im currently doing a EICR report they have a socket in a airing cuoboard which used a to have a shower pump plugged now has the vacuum.charging. the distance from the bath is well within zone 2 but is in a seperate cupboard what C classification would you give this?
 
If cupboard needed a tool to open then that's ok. But I'm not sure it's the same as putting it otherside of the bathroom door ?
With my tin hat on, I'd be tempted to C2 it as if the cupboard door was not there ... BTW, is there an RCD ?
 
The extent of the special location is limited by the airing cupboard doors
With that in mind the socket location is fine

If on the other hand you were installing sockets and felt personally that you need to account for a idiot plugging an item in an airing cupboard or landing socket and hoovering their hair whilst playing in the Bath then advize accordingly :)
 
I haven't looked this up, am not disagreeing with the views given and not being near to a set of Regs where does it state zones do not include cupboards.
As far as I know the regs only state that no sockets shall be within 3m of the boundary of zone 1.
I know of no reg that exempts the inside of a cupboard from being part of the special location.
 
As far as I know the regs only state that no sockets shall be within 3m of the boundary of zone 1.
I know of no reg that exempts the inside of a cupboard from being part of the special location.
Yes I was thinking the 3m part but the cupboard rang no bells, so from this I would conclude there should be no socket there?
 
Yes I was thinking the 3m part but the cupboard rang no bells, so from this I would conclude there should be no socket there?

I would conclude this too. Can anyone who posted above who advised no code provide reasoning behind this ? Seems to be a commonly held view so there must be some basis in official guidance at least.
 
As far as I know the regs only state that no sockets shall be within 3m of the boundary of zone 1.
I know of no reg that exempts the inside of a cupboard from being part of the special location.

That's knackered my landing socket then. I'll have to remove it :)
 

Reply to Socket in airing cupboard in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

  • Question
There is also the ongoing problems if this is a gendered changing room.... For example, 2 or 3 burly male soldiers (you said it was an officers...
Replies
5
Views
875
  • Question
ok cheers for the help lads
Replies
7
Views
704

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top