5A BS1362 in a spur you say ?
pointless , in the event of a fault it will blow a week after a 6A mcb lol.
use a 3A max fuse in the spur with a 10A type B or a 6A type C at the CU and you might get some discrimination.
Unless you've got rewirables at the board , in which case you've got at least 20A to play with.
;-D
pointless , in the event of a fault it will blow a week after a 6A mcb lol.
use a 3A max fuse in the spur with a 10A type B or a 6A type C at the CU and you might get some discrimination.
Unless you've got rewirables at the board , in which case you've got at least 20A to play with.