Socket Tester Neutral Fault | Page 2 | on ElectriciansForums
Discuss Socket Tester Neutral Fault in the UK Electrical Forum area at ElectriciansForums.net
Cornwall
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three green lights came on saying everything was fine and correct. When I took the faceplate off to do my R1 R2s I got readings of 0.60 on R1 but then >2000 on Rn. I know socket testers shouldn't be relied on and I only use it to see if there if anything obvious before I take the faceplate off but surly it should of shown a natural fault?
it only tells you the polarity is correct, it isn't for readings and is an indicator only, no different from a volt stick, both convenient but unreliable really.
Only if you run a test, it won't by just plugging it in.
I often run the no-trip Zs as a quick check, as it verifies all conductors look OK and if N-E swap then RCD trips on the high current PSCC side.
But more generally as N & E are electrically so similar there is not any trivial check without added work, like isolating the N at the CU.
Reply to Socket Tester Neutral Fault in the UK Electrical Forum area at ElectriciansForums.net
Very technical :D