Dizzy_Maskell

Guys please back me up on this, went to a mates house and he has "proudly" shown me his DIY electrical handy work,

Few years back I ran a swa cable to the bottom of his garden tapped off the outside light as he wanted a light at the far end of the garden to for his shed etc.

He has adapted it now and added sockets to the shed for bits a pieces. But he has to turn the outside light on for them to be energised.

As he only uses the sockets whilst he is down there and so needs the light on anyway "there is no problem" can someone back me up so I can show him please as my qualifications don't appear to count.

Main switch 61008 on Con Unit and outside light circuit fed from down stairs lights 60898 B6.

Cheers
 
Show him Table H2.1 of your on-site guide, A2 Radial. Explain that his circuit is a type of radial and that it needs to be a 2.5 cable for him to have sockets.

Or, is it a fused connection, see H2.3..."Where a fused spur serves socket-outlets.....

What thread you on mate.... im confused
 
Show him Table H2.1 of your on-site guide, A2 Radial. Explain that his circuit is a type of radial and that it needs to be a 2.5 cable for him to have sockets.

Or, is it a fused connection, see H2.3..."Where a fused spur serves socket-outlets.....
No mate, the dozy customer has stuffed some 13amp sockets on the end of a bit of 1.5mm which is feeding an outside light switched from the house, I really don't see what all the fuss is about.

The OP did the original job which was to install an outside light, and his mate(the customer has done the dirty deed with the socket abortion)

The OP has asked for advice on what he should tell his mate, and has received a lot of good advice. There is nothing more he can do, perhaps if he showed him all these threads that may make him see sense, although I doubt it/
 
No mate, the dozy customer has stuffed some 13amp sockets on the end of a bit of 1.5mm which is feeding an outside light switched from the house, I really don't see what all the fuss is about.

The OP did the original job which was to install an outside light, and his mate(the customer has done the dirty deed with the socket abortion)

The OP has asked for advice on what he should tell his mate, and has received a lot of good advice. There is nothing more he can do, perhaps if he showed him all these threads that may make him see sense, although I doubt it/

Aye well .... you can lead a horse to water, but a pencil must be lead. ;)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Socket wired of a outdoor light!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
48
Unsolved
--

Advert

Thread statistics

Created
Dizzy_Maskell,
Last reply from
Geordie Spark,
Replies
48
Views
5,223

Advert

Back
Top