Little scenario for you all.

I've been doing an eicr today and come across a double socket wired as a radial on a 2.5mm t-e, which is protected by a 32 amp rcbo.
Technically this cannot overload as the cable can withstand 27 amp ref method c. Unless mr DIY comes along and starts adding new sockets which I am not responsible for so my question is would you leave it
 
The op of this thread EICR different story, BUT to create a radial 2.5mm backed by 32amp mcb, come on basic electrical craft principles never mind 1.5mm, and all this talk about relying on fused appliance's to protect the CIRCUIT against overload current is crab.!!!
 
I certainly wouldn't advocate the scenario, and have always worked on the basis of MCB egual or less than CCC of cable. I have always replaced 'offending' MCB's in the past with something more 'suitable' but maybe I've been over cautious? I don't get involved with EICR's so don't have the dilemma of which code is 'appropriate' :)

I wouldn't say that.. I'd say "sensible". :smile:
 
Ok i will just use any breaker i have spare in the van for any circuit then provided its fused at the end of the circuit somewhere

The cable would be protected against overload - IF

It only served one piece of equipment at the end of it's run and nothing on the way, so you can't have a radial with 3 double sockets on it obviously.

Obviously you can't have a 16A socket at the end because these have no fuse system, but you could have one 13A socket or one switch fuse (fused appropriately for the cable)


I am not saying I go out of my way to install like this, I use an appropriate sized MCB at the origin like anyone else, but technically you don't have to.
 
Ok i will just use any breaker i have spare in the van for any circuit then provided its fused at the end of the circuit somewhere

But then you are giving no consideration to thermal constraints...

Producing extreme and ridiculous examples does nothing to contribute to this debate...IF overload and thermal constraint limitations are met, it complies with BS7671 so no code, no comment :13:

Why do you think it is acceptable to install a 2.5 spur from an RFC?
 

Reply to socket in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
793
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top