Sockets on a radial circuit
Hi all,
After some advice here to settle my mind, is there any regulations to limit the number of sockets on a 20A 2.5mm radial? Reading regulation 433.1 i know it states 50m² floor area, but i can't seem to find anything about the number of sockets? Or is it just the total load that determines this?
The reason is, i have been asked to install some sockets, 10 in total, for means of flexibility of plugging appliances in around the area, I'm being told that the sockets will be used for power tools, chargers, a computer and occasionally a heater.
Any information to help clear this up is appreciated.
For information only, the French Regulations allow twelve sockets on a 20amp MCB 2.5mm radial
UK 20m2 (4m x 5m room). A room that size would have around 6 doubles, so not a great deal different.
I assume that if it's known that the sockets are going to be heavily loaded, then design considerations would override the general rule, just as in the UK.
Except for the amendment a couple of years ago where you could instal twelve doubles, forgot to mention the regs only allow for six sockets in a Kitchen above the worktop in 2.5mm, and appliance's have to be on their own 2.5mm 20amp radial.
The answer, I think, is more a practical one than theoretical - at some point you'll run out of allowable Zs!!
From the OSG 4mm on 32A B is limited to 43m on VD (really 86m if loads are evenly distributed, as they probably would be with multiple sockets over a couple of rooms) and potentially much less on Zs (if, like me, you really don't like the idea of depending on the RCD for disconnection). Then it has 28m on TN-S typical max Ze
For comparison a RFC with 2.5mm on 32A B is 106m / 96m
For the OP's original 2.5mm & 20A probably around 84m on VD (distributed load) and 60-70m or so on Zs?
The true answer is provided in the Design Guide....
If you DID put 500 sockets in, you'd save on cable length...but your wrist would ache from making all the terminations...
and it would be rather more costly
Just been doing a loft extension with a client who really likes sockets.... A child's fairly normal size bedroom with 12 sockets - I think he wanted them near the bed, but couldn't decide where the bed was going!
Also 4 round pin sockets on the light circuit in the master bedroom, while will probably never get used....
I did put in 2 x 20A radials for 4 upstairs bedrooms when I might well have only gone with one in a 'normal' installation.
Other than slightly increased initial costs, I can see only benefits to running several circuits where tradition might dictate that one would suffice.
Less inconvenience in the event of a fault. Less time involved in fault finding, should future issues arise. Reduced likelihood of a broken neck when extension leads are used in place of diagnosis and repair...
If AFDDs are required in AMD2 then I can see new builds going back to as few circuits as possible!
Stephen-d,
mydigitalhome,