Mark6098

2 sockets on dado trunking within half a metre of each other, would you agree on warning notices for potential 400v?
 
Agreed also. I would not label sockets now that there is no requirement to do so. Lots of so-called electricians don't understand where the 400V comes from so the average user won't have a clue. Labels that don't convey useful information are a menace and cause confusion. I saw a similar situation in an office where a 6-way plastic gridswitch on a new install had a 'Danger 400V' label stuck on the dado trunking next to it. The office staff were pushing the switches with a plastic rule because no-one knew what the danger actually was!

Stage lighting is a bit of an exception because the sockets are normally intended for use by instructed persons. We used to do the Trafolyte channel labels in the appropriate colours but you can't see the difference with harmonised colours so use the numbers now.

We still do, on some of our installation areas, but for ckt identification purposes, not for any form of 400V warning.... They seem to have labels for just about every situation now in the UK, most of them totally pointless and at worst (as you say) confusing!!
 
I think some of these people need to visit some industrial or large commercial premises to see for themselves, that it's not only common, but is standard practice!!

In this instance (OP's situation) it's an office installation, and would be a perfectly acceptable and normal method of wiring large amounts of socket outlets across a 3 phase supply....


Yes but what I was referring to as being less common is having to install closer than 2M between in an office/IT room (op) - so requiring the label (pre 17th am 1)
 
Doesn't matter mate, they can be next to each other (and often are), compliance with safe isolation practices, will always negate any perceived or real risks....


Fully agree - never argued anything different other than how common they are closely positioned in the OP type install - but we all have differing experiences
 
The worst one I ever came across was in a training centre for electricians,a single metalclad socket below a DB,connected to this by a coupler and 2 bushes was another single socket,now one was fed off red phase and one off yellow phase,with both sets of feeds going through the first box.I commented on it to one of the instructors who replied "it'll be ok one of us fitted it so we know about the way it's done"
 
why would you need warning signs?? for what?
In the event of simultaneous line to earth faults on appliances using these socket outlets, the metalwork on both would rise to mains voltage until the protective device for each has operated to clear the faults. This is highly unlikely, but is possible. If it did occur, shock voltage when the metalwork of both were to be touched simultaneously would be 400V, not funny.
 
In the event of simultaneous line to earth faults on appliances using these socket outlets, the metalwork on both would rise to mains voltage until the protective device for each has operated to clear the faults. This is highly unlikely, but is possible. If it did occur, shock voltage when the metalwork of both were to be touched simultaneously would be 400V, not funny.

Note, thread is 8 years old.
 

Reply to Sockets on different phases in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top