laxmi

Hi,
How can I change earth resistance (R) value into soil resistivity (Rho)? Is this formula correct, ⍴ (Rho) = 2πAR (A = Distance between pegs, R = Earth resistance).

Regards,

L.
 
Hi - this is the simplified eqn for use with the Wenner Method, which to be accurate would need R to be found from using the Wenner layout of probes for current and voltage. But I'm not an expert ...

IMG_0469.jpg
 
Yes agreed, you cannot simply use a 2-wire resistance measurement because that will include the contact resistance of rods / probes. The 4-wire measurement to obtain Rw eliminates this and only measures the resistance resulting from the bulk resistivity of the soil.
 
Thanks for your information, it was very usefull for me.

Can we not use earth resistance value (R) that is measured from earth electrode test method, to obtain soil resistivity. I have measursed existing earth electrode and value is 80 Ohm.

Does it not give us soil resistivity using formula ⍴ = 2πAR

Your advice will be much appriciated.

Lax
 
Hi - if I understand correctly you have a measured value for electrode resistance. This will be as accurate as the particularly method allows and different methods will likely lead to different results as some are more accurate than others.

Using that eqn with your electrode resistance result you will get a number, but it is unlikely to accurately represent resistivity as per LN post#3 reasons.

Can I ask why you need resistivity?
 
Hi,
Thanks for your further assistance.

I am calculating substation earthing system. Existing earthing system was intalled approx 30 years ago. I can go for one for one replacement with similar earthing type but factirs might have changed by this time. And it is also good to know all information before hand.

Please see the formula, in which soil resistivity value is required.

Regards

IMG_9048.JPG


IMG_9048.JPG
 
Got it - GN8 if I'm not mistaken. For your purpose I would recommend you seek out the proper resistivity measurement kit and perhaps read up on their reference BS7430.

Just for fun as its -5C here this morning, I'm imagining I'm on a desert island with this challenge and no kit. I would estimate rho as you propose, design an earthing system using it, instal it, measure R actual, adjust rho in light of this result, design another system with say twice as much surface area, instal it, measure it and confirm R actual was as per design from rho estimate.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Soil resistivity
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
laxmi,
Last reply from
Wilko,
Replies
6
Views
1,824

Advert

Back
Top