I have a question as I can’t get my head around something with solar PV
I’m going to be working on a new build in a couple of weeks as the contractors have installed the electrical installation incorrectly as per the customer request when buying and are now refusing to correct. There’s been some ongoing discussion between the owner and the builder but each are arguing from different points of view. So I’ve been asked to go in and sort it.
The problem is regarding the feed to a garage supply.
At the moment the garage is fed from a 50A MCB on one side of a split load board. Which then runs in 10mm SWA to a garage board where they have put a 32A MCB for the EV charge point
However under Amdt 2 and 722.531.3.101 this is not compliant as EV Charge Points have to be on their own dedicated DP RCD protection, with no other circuits, if it’s not built into the unit itself. The unit I’ll be installing doesn’t have inbuilt 30mA protection. I know they will be working to Amdt 1 as that will likely be the house design spec. But they have put a SPD board in (which is not necessarily a requirement under Amdt 1 if the CRLS doesn’t deem it so) so they’re kind of working to it in areas where they want and not in others.
So my options are
1. Create a non-RCD way in the board and feed the garage. Then install a RCBO board in the garage. Thus giving the EVCP its own dedicated protection. But I am not sure if this is possible until I remove the cover as it’s a BG board and if RCD one shares its neutral with the main incoming neutral bar then it may have to be option 2 anyway. Or get DIY Dave creative with Wago’s.
2. Split the tails, install a small 2 way enclosure and a 50A DP MCB and then a RCBO board in the garage.
However the customer wants to get proper solar PV and Battery Storage (there is a paltry 3 panels on the roof to ‘tick a box’ from the build).
So, as I don’t fully understand how solar works. If I go with option 2 and split the tails, so as not to use up one of the two remaining spare ways in the board. Will this mean the garage doesn’t benefit from the PV and Battery storage?
If that’s not the case and it will can someone explain to me how with split tails the garage would benefit from the PV & BS if they’re installed in the main board? As I can’t work out how the CT clamp would see the garage load unless they install it on the tails from the meter itself. But still then unsure how it would feed the garage as they would only be linked via the Henley block.
If I’m being dumb be gentle. I’m working 7 days a week at the moment and just can’t work out how the solar and PV would work with split tails.
Thanks
Carl.
I have a question as I can’t get my head around something with solar PV
I’m going to be working on a new build in a couple of weeks as the contractors have installed the electrical installation incorrectly as per the customer request when buying and are now refusing to correct. There’s been some ongoing discussion between the owner and the builder but each are arguing from different points of view. So I’ve been asked to go in and sort it.
The problem is regarding the feed to a garage supply.
At the moment the garage is fed from a 50A MCB on one side of a split load board. Which then runs in 10mm SWA to a garage board where they have put a 32A MCB for the EV charge point
However under Amdt 2 and 722.531.3.101 this is not compliant as EV Charge Points have to be on their own dedicated DP RCD protection, with no other circuits, if it’s not built into the unit itself. The unit I’ll be installing doesn’t have inbuilt 30mA protection. I know they will be working to Amdt 1 as that will likely be the house design spec. But they have put a SPD board in (which is not necessarily a requirement under Amdt 1 if the CRLS doesn’t deem it so) so they’re kind of working to it in areas where they want and not in others.
So my options are
1. Create a non-RCD way in the board and feed the garage. Then install a RCBO board in the garage. Thus giving the EVCP its own dedicated protection. But I am not sure if this is possible until I remove the cover as it’s a BG board and if RCD one shares its neutral with the main incoming neutral bar then it may have to be option 2 anyway. Or get DIY Dave creative with Wago’s.
2. Split the tails, install a small 2 way enclosure and a 50A DP MCB and then a RCBO board in the garage.
However the customer wants to get proper solar PV and Battery Storage (there is a paltry 3 panels on the roof to ‘tick a box’ from the build).
So, as I don’t fully understand how solar works. If I go with option 2 and split the tails, so as not to use up one of the two remaining spare ways in the board. Will this mean the garage doesn’t benefit from the PV and Battery storage?
If that’s not the case and it will can someone explain to me how with split tails the garage would benefit from the PV & BS if they’re installed in the main board? As I can’t work out how the CT clamp would see the garage load unless they install it on the tails from the meter itself. But still then unsure how it would feed the garage as they would only be linked via the Henley block.
If I’m being dumb be gentle. I’m working 7 days a week at the moment and just can’t work out how the solar and PV would work with split tails.
Thanks