I think that would be a departure from the regulations, but would obviously require design justification.

I should think solar installs are a bit different anyway as the inverter is the source of the supply, not the load!
 
Yes, but it is still a source of supply at those times, that is the whole point of the system!

As far as I know multiple sources running in synchronisation need to have a single common earthing system.
 
Looks as if the two smaller cables in that panel are SY cables ( those with the braided earth link between them) which is a no-no for external cabling before you start to worry about the earthing system....

Is there no ''Approved'' distribution/layout drawings available for this solar farm installation, at least then you'd know what the system design concept is or was, and if it has been altered by others??
 
yes that is sy going to the inverters but i know that that is wrong but thats not part of what i have been asked to do at the moment.is there a reg that disalowes sy out side or is it just the manufactures specification?

i havent seen any drawings just been instucted by a consultant from the firm that built it because the company that will be running it wont exept it as it is. when i have questiond what they have asked me to do ive just been told to get on with my work.


the earth wire goes to one of the steals that support the array
 
How the hell can you assess this new build solar farm's electrical installation without having the access to the drawings to which it was built too??

EDIT... What work remit exactly have you been instructed to carry out to this Solar Farm and why isn't a technical representative of the company that built it, not come to site to check for themselves what deficiencies (if any) are existing on this installation?? I don't suppose you know the details either, of why the other company are not
accepting the the installation as it stands??

Something sounds a bit fishy here!!

Manufacturers cable description will give you that, these SY cables are not UV protected and the outer transparent sheath will soon start to deteriorate. Some manufacturers will even state not to be used as prime current carrying conductors, they are designed in fact for control/machine wiring and the like....
 
Last edited by a moderator:
Last edited by a moderator:
IMO the installation is unsafe, unfit for purpose, should be immediately disconnected until redesigned and reinstalled by someone who knows what they are doing.

loplug, you cannot fix a broken leg with a sticking plaster.

i agree it should be redesignd and reconnected i cannot see them disconecting it as that would cost them money.

who broke there leg?

does any one know what the normall or an exepted methood of connecting the inverters to the supply?
 
I'll ask again, ...What work remit exactly have you been instructed to carry out to this Solar Farm
 
Just to change the connection in the boxes from the first picture to the second picture. So disconnecting the earth neutral from the 4 pole isolator and resleaving then strip the blues leaving from the 95mm
 
Well without access to any drawings you can't very well say too much. I'd get on and complete the work contracted to undertake and submit your invoice, perhaps giving some written notice of anything that you consider as deficiencies that you have found. It's then down to this other company that is going to be responsible for the running and upkeep of this solar farm installation, if they are now happy or NOT with the limited remedial work you have provided?? .. lol!!
 

Reply to the thread, titled "Solar farm earthing" which is posted in Solar PV Forum | Solar Panels Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cornwall

Thread Information

Title
Solar farm earthing
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
loplug,
Last reply from
Engineer54,
Replies
26
Views
5,933

Advert

Back
Top