Thank you for your help. Our solar system is functioning as expected (our electric meter and solar meter are both in the living room, we have created 701kwh since our last feed in statement; one due now and this is In line with what we have made at this time of year in previous years. The electric meter shows red (no power being used from the grid) for most of the day apart from the obvious when kettle or electric oven is on - we have never used huge amounts of electricity as a family so the iboost has always worked well for us until now.... The sender is flashing a green light to indicate working and the clamp is on the right way (had that issue a few years ago when an electrician came to replace our old meter and attached the clamp upside down). The wire from the sender to the clamp seem ok. Could the clamp itself be faulty? With the main iboost unit, we normally leave this switched on permanently via the mains switch, even when we go on holiday as the unit heats the hot water and switches off when hot. When we first noticed a few weeks ago that the water was not very hot despite a sunny day, we did the typical cure used on electronics and turned the iboost off at the power supply, counted to 10 and turned it back on. The iboost then started heating the hot water with the excess power being generated but this then slowly decreased until 0. When the previous replies we were thinking that maybe the power supply from the mains socket to the iboost is faulty / not supplying enough power but have no tools to check this. Do the iboosts have a life expectancy? Ours was installed a few years ago around 2016/2017; I can’t find any paperwork to confirm but I know it was a little while after the solar panels which were put in 2015Hi, just seen this thread and my be able to offer some help, shame on the information you have received so far though.
Firstly, what you describe is normal start-up behaviour for an iBoost. When it is first switched on it displays "Low Voltage" (reasonable, there was no voltage) then the software version and then it briefly provides power to the tank to check that that works. Indeed, if you switch an iboost on at night, that is exactly what it does, so it seems unlikely that you have anything wrong with the main iBoost unit.
The symptoms you describe are, however, consistent with the iBoost sender believing that there is no spare power to divert to the immersion heater and this points to the sender unit (or worse). The sender measures the current (power) being fed back into the power grid (exported) and gives that information to the main iBoost controller so that it can adjust the amount of power it sends to the tank, aiming to always export a little.
We know your sender unit is talking to the main iBoost controller so communications are not the problem. So immediate thoughts are:
a) hate to say it, but is your solar system generating as it should be and generating the expected amount (don't know your details so can't be more exact)
b) now check that the thin cable from the send to the current clamp (the square block that clips to your live power feed) is undamaged
c) check that the current clamp is firmly clipped on the right mains input cable. This must be the live feed from either the utility company fuse or isolator switch. The current clamp has a latch on it to be able to fit or remove it and this latch must be firmly closed so the clamp tight right round the relevant cable
d) if the current clamp has been removed for any reason do check that it has been put back on the right way round (yes, it needs to "face" the right way!). If you want a picture of a clamp in position just ask.
d) And if none of these things apply then suspect that the sender has died - but that seems unlikely.
Hope that helps before you run up too many bills.