Daf Thomas
About a year ago we installed a 3.99kW PV system to a farm shed roof. We used a sunnyboy SB4000TL-20 inverter and used 2 strings, 1 of 11 and 1 of 10. Up until a month ago it had worked fine since we installed it, but now during midday when the sun is strong the inverter stops working. Ive been back to see whats happening and it appears that each string makes the AC voltage rise by 4 volts. The supply voltage at the property is allready quite high at 254 volts so when both strings are on during sunny periods the voltage coming back through the AC side of the inverter goes up to 262 volts which knocks it off. The supply from the house to the shed is 10mm run over 70M.
Any suggestions on what is making the voltage go so high, or how to fix it? Or is it something like the inverter has gone faulty?
Thanks
Any suggestions on what is making the voltage go so high, or how to fix it? Or is it something like the inverter has gone faulty?
Thanks