Solution needed!!!!…I used a Contactor instead of an ATS to connect 2 power sources (main and ups) for power redundancy | on ElectriciansForums
Discuss Solution needed!!!!…I used a Contactor instead of an ATS to connect 2 power sources (main and ups) for power redundancy in the UK Electrical Forum area at ElectriciansForums.net
India
I used a Contactor instead of an ATS to connect 2 power sources (main and ups) for power redundancy and the output is connect to a Dell server. i.e, if main power is lost contactor will changeover to ups power and there should be continuous power supply for the dell server…
but i have a problem!!!
.during changeover my Dell server turn off (restarting). I think this is due the switching/changeover delay of the contactor…can someone help and propose the best solution..
Why aren't you feeding power to the Ups and the ups to the server?
Reply to Solution needed!!!!…I used a Contactor instead of an ATS to connect 2 power sources (main and ups) for power redundancy in the UK Electrical Forum area at ElectriciansForums.net