G
GStueyXR
here is my solution... and a definitive one too :)
cable is 80m @ 1.87 mΩ....
Resistance of line conductor= (80 x 1.87) / 1000 =0.15 Ω
Load is 45A. Expressed as a resistance 230/45 = 5.1 Ω
Resistance of Neutral conductor= (80 x 1.87) / 1000 =0.15 Ω
Total circuit resistance of 5.4 Ω
42.6A would flow in this circuit
So we have 3 resistors in parralel.
--------| 0.15Ω |-----| 5.1 Ω |-----| 0.15Ω|-------
Vdrop across Line conductor would be ----- 0.15 x 42.6 = 6.4V
Vdrop across load would be ------------------- 5.1 x 42.6 = 217.2V
Vdrop across neutral conductor would be --- 0.15 x 42.6 = 6.4V
So, Vrop in circuit conductors would be - 12.8 V
Would you agree with these calcs ???? If so, I got it wrong on the night... I got 13.5 Vdrop....
Dont know how I got this wrong... It is afterall very basic stuff
depends very much on the wording of the actual question - what is the value 1.87m ohms? is it a an (R1+Rn)/metre for a twin core cable or for just a single core cable. Usually it is for a twin core cable in which case it is just
Vd = Ib x L x m ohms/m
1000
= 45 x 80 x 1.87
1000
= 6.73V
and you don't worry about the neutral.
Also as Lenny said if temperature is mentioned it could just be that there are correction factors to applied to the resistance value
Wrong in my opinion.
If there was no PD in the neutral, then current cannot flow. since current is eqaul at all point in a circuit there must be a potential between the termination at load, and the center of the supply transformer.
Every circuit is basically 3 resistors in series.... The line conductor resistance, the load, and the neutral conductor resistance.
I think you are thinking about it too deeply.
As i said it all depends on what that 1.87 figure represents - did it say for a single or a twin core cable? If it is the latter then in all likelyhood you forget the neutral.
don't know if you saw my reply to an earlier post of yours but mV/A/m is resistance per metre.
I totally messed this question up the only chance of a mark I have on this one is for putting 5%
26
Durig the course of the inspection one of the single phase radial circuits supplying an item of fixed equipment is to be checked for voltage drop compliance. the circuit has the following charicteristics
. load current =45A
. circuit length =80m
. live conductors =10mm
a) using the info in fig 1 1.83 for 10mm determine wether the circuit meets the requirments for voltage drop.
show all calculations
b) state
i) a suitable observation to be recorded on the periodic report. if the voltage drop fails to comply
ii) one action which could be taken to rectify the situation in b)i above
cheers:)
I see it says" line conductors" so i would multiply length by 2 to take account of neutral in this case.
yeah mate i only knew how to do it by mv/A/M X IB X L divided by 1000
but as there was no mv table something was niggling at me saying it was something to do with V=I X R
but i proceeded to work out the resistance by M0hm/M X L divided by 1000 ie 1.83 x 2 x 80 divided by 1000
= 292.8 divided by 1000 = 0.2982OHm = 0.3 ohm then from there not sure if i put 0.2982 X 45 =13.419 = 13.5v 0r 0.3 x 45 =13.5v
then went onto mess the next bit as it asked for a observation and i put something like its not acceptable instead of saying volt drop to high to comply with 5% ie 11.5v
and for last bit of question where it asked what you could do i put increase csa of conductor
head had gone completly by then just hope i did enough earlier on
Formula to use is
2 x L x Ib x R /1000 = VD
2 x 80 x 45 x 1.87 /1000 = 13.464
Formula to use is
Hope you are right mate.... I did this through intuition, after a 5 minute think.....
But now I doubt myself as you can see in the OP
Solution to 2391 Q26 (june 10 paper)
GStueyXR,
TPES,
TrueNAS JBOD Storage Server