D
davesparks
Cable is all 1.5mm^2
Wago boxes are all 20A or 40A. Switches are motion sensing - rated nowhere near 20A.
I will try a 16A breaker to see if that resolves it - at least until I replace the CP.
Otherwise I will need to replace CP now, in order to use a C-type breaker. I was trying to avoid replacing CP right now because I’m sure I will need to make modifications when the inevitable car charging port needs to be installed.
You can't just swap in a C type MCB or even a higher rated one.
You need to confirm that it is safe to do this, including checking that the earth fault loop impedance is low enough to be safe with a different MCB.
If the switches are not suitably rated for these changes they may also need to be replaced.
I suspect that this line from your opening post:
Is at the root of your problems.I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs)