exam answer.

if you have a Zs that is too high on a cicuit protected by a B type Bsen60898 MCB, then youhave the followibng options, assuming no loos connections, as by this time you woul have already carried out all dead tests, and ruled that out.

a) Replace MCB with an RCBO to bsen61009
b) Replace CPC with one of a larger CSA.
c) Rewire the circuit.
d) use supplementary bonding to reduce your Zs.
e) reduce the length of the circuit
f) if the MCB is overrated for the load, then reduce the rating of the MCB.

end of exam answer

ifthere is little differencee between the measured Zs and the corrected Zs is minimalm, then you may carry out more detailed calculations to arrive at a more accurate figure otabulated Zs, in otherwords more accurate than the rule of thumb.
Also, Loop testers are affected by noise on the electrical system, and you may find that Zs= Ze +R1+R2 is a better method arriving at Zs. You will probably notice this, as your measured Zs will be higher than the above calc, and it should be the same, or lower (90% of the time lower)
 

Reply to Solutions to Zs too high in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
970
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top