Hi Tennisball,

Page 11 at the bottom of the green OSG. I'm fairly new to this all as well, but my interpretation was 200ohms, 21ohms being something different that I am not sure about (hence question above)

Basically anything TT needs an RCD to meet disconnection times, although a lot of TT have 100ma RCDs supplied by DNO so where do they sit in the reg's with disconnection times? I presumed it was the same as 30ma? (0.4sec)
 
Last edited by a moderator:
Yep sorry was just refering to the OP original post



Not quite sure what the OSG means by 21ohms being the usual max stated resistance of the distributors earth electrode at the supply transformer, is this something you would see out on a domestic job as I don't think I know what a TT with distributors earth before if thats the case? How would you tell, would there be an earth following the incoming tails from overhead lines or similar?

I found the text you are referring to on page 11 osg.

Yes it is confusing. The way I understand it is we are supposed to install an earth electrode at the consumers location with as low an impedance as possible. This would obviously be much more difficult retrospectively.

But the impedance measured between the consumers earth electrode and the dno's transformer must not exceed 21 ohms.

Has anyone ever installed a TT earth rod? How do you test the earth path between transformer and the consumers transformer?
 
Hi Tennisball,

Page 11 at the bottom of the green OSG. I'm fairly new to this all as well, but my interpretation was 200ohms, 21ohms being something different that I am not sure about (hence question above)

Basically anything TT needs an RCD to meet disconnection times, although a lot of TT have 100ma RCDs supplied by DNO so where do they sit in the reg's with disconnection times? I presumed it was the same as 30ma? (0.4sec)

This is a giant can of worms if I ever seen one!!!
 
the 100mA RCDs installed at the front end of a TT installation were to achieve disconnection times in the event of a fault. the max. Zs for these devices is 500 ohms ( see table 41.5 )
 
Thanks telectrix, providing disconnection time is met, it is OK to leave 100ma as method of ADS, providing installation does not require 30ma due to installation methods (cables in wall >50mm etc), right? Or have I missed something ?


Also how do you interpretate the 21ohm statement re TT installations in OSG, what exactly are they refering to?
 
Last edited by a moderator:
Yep sorry was just refering to the OP original post



Not quite sure what the OSG means by 21ohms being the usual max stated resistance of the distributors earth electrode at the supply transformer, is this something you would see out on a domestic job as I don't think I know what a TT with distributors earth before if thats the case? How would you tell, would there be an earth following the incoming tails from overhead lines or similar?
the earthing conductor would not be connected to the sheath of a tns system and would not be connected to the neutral in the Head it would run of to a earth electrode somewhere in garden
the 21 ohms is the suppliers side at the earth rod at the transformer end
200ohms is the max from consumers earth electrode to the suppliers
but as Tel say try to get a reading around 100ohms or less and the rcd 30mA is for if you fail to meet the max Zs for the circuit from RA X by i delta n ie 30mA rcd which is 0.03A is less than or equal to 50v
Ra is the sum of reistances of the earth electrode and the protective conductor(s) connecting it to the exposed conductive part

to find the max of any rcd its Ra divided by I delta n Ie 30ma
50 divided by 0.03A gives you 1666.666667 which when rounded up gives you the max Zs of 1667ohms
a 100mA rcd
50 divided by 0.1 = 500ohms
a 300mA RCD
50 divided by 0.3 = 167 ohms rounded up
a 500mA rcd
50 divided by 0.5 = 100 ohms max

idelta n is the rated residual operating current
if it was a TN system then its
Zs xIa is less than or equal to Uo
Ia is the current in amperes causing the automatic operation of disconnecting device within the time specified by the relevent table 41.1 was pg 46 in the BRB now pg 53 BGB

tables 41.2 are for fuses 0.4 disconnection time 41.3 is for Circuit breakers 0.4secs 41.4 are for fuses with 5secs disconnection time
table 41.5 is for rcds and rcbos

A TT system has a max of 200 ohms at consumers earth electrode then it uses General mass Of earth to reach the suppliers Earth elaectrode which they guarantee will not be more than 21 ohms
then the suppliers earth electrode is connected to the star point of the transformer
TN-S uses the sheath and is seperate in consumers side and suppliers side and has max of 0.8
TN-C-S has a seperate earth in consumers side but then connected to the neutral in the suppliers head and from the neutral and earth are combined using a protective earthed Neutral (Pen conductor) all the way to star point and there will be earth electrodes along the way ie PME Protective Multiple Earthing
hope that makes sense and hopefully i have it right as last time i said all that was for me 2391 exam june 2010 lol
 
Last edited:

Reply to Some Advice On Testing If you will......... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
935

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top