Hello all,
I have recently begun carrying out more I&T jobs and have a few questions that I wanted to put to the forum.
1. Why are Zs readings, taken at the main switch disconnectors at distribution boards fed via UPS systems so high and how do these readings satisfy maximum permitted Zs values from their respective MCB?
2. When carrying out the safe isolation process, can a low resistance ohm meter be officially used in place of a voltage indicator/test lamp in order to prove that supplies are live or dead.
3. How is it determined what sizes the main protective bonding conductors should be that are supplying the respective gas and water supplies at additional buildings on a large multi building site? Are they conducive to the sizes of the main cables that supply the said additional buildings? (the same principal as the main gas and water supplies in the primary building).
4. If it is found that a lighting circuit has a cpc installed but has gone missing at a particular light, should this be noted as a C2 or C3 observation? (assuming the light is just a plastic pendant).
5. Is it permissible to have 3x2.5mm csa cables connected into the MCB of a 32A ring circuit if one has been tested and confirmed to have been used as radial tap off? 3 cables is obviously permissible at a socket or spur point so is it permissible if it is terminated at the MCB or would it be deemed as an overrated circuit?
6. If a radial socket or spur is bolted onto a distribution board (meaning the cable run of the circuit is contained within the board and also of a very short length) does it matter if the cable size is too small for the MCB that is protecting it or would it be classed as overrated? (the same as any other circuit).
Questions 5&6 in particular I've heard very mixed opinions about from other engineers so any clear feedback on these issues would be welcome.
Cheers for reading all.
I have recently begun carrying out more I&T jobs and have a few questions that I wanted to put to the forum.
1. Why are Zs readings, taken at the main switch disconnectors at distribution boards fed via UPS systems so high and how do these readings satisfy maximum permitted Zs values from their respective MCB?
2. When carrying out the safe isolation process, can a low resistance ohm meter be officially used in place of a voltage indicator/test lamp in order to prove that supplies are live or dead.
3. How is it determined what sizes the main protective bonding conductors should be that are supplying the respective gas and water supplies at additional buildings on a large multi building site? Are they conducive to the sizes of the main cables that supply the said additional buildings? (the same principal as the main gas and water supplies in the primary building).
4. If it is found that a lighting circuit has a cpc installed but has gone missing at a particular light, should this be noted as a C2 or C3 observation? (assuming the light is just a plastic pendant).
5. Is it permissible to have 3x2.5mm csa cables connected into the MCB of a 32A ring circuit if one has been tested and confirmed to have been used as radial tap off? 3 cables is obviously permissible at a socket or spur point so is it permissible if it is terminated at the MCB or would it be deemed as an overrated circuit?
6. If a radial socket or spur is bolted onto a distribution board (meaning the cable run of the circuit is contained within the board and also of a very short length) does it matter if the cable size is too small for the MCB that is protecting it or would it be classed as overrated? (the same as any other circuit).
Questions 5&6 in particular I've heard very mixed opinions about from other engineers so any clear feedback on these issues would be welcome.
Cheers for reading all.