Hi I really need some help here! I am still new to this stuff

In carrying out the inspection tests : Ze, PFC, PSCC, and Polarity of the supply, do we re energise the installation ie. replace back the supply fuse (i.e. the 100 Amps fuse). Or do we only turn the main switch ON in the consumer unit. Also what about Zs do we reinstate the supply fuse (100 Amps fuse) or do we only turn the supply ie. Main switch back on?

Thanx a million
 
yopu cant re energuise the supply by just flicking the main switch, if the fuse is still out. When re-energising, turn the main switch to your board off! all MCB's/RCBO's off. Insert main fuse into holder. Turn main switch to CU on. then turn on each circuit on, one by one, providing it is safe to do so1

John
 
In what way are you new to all this stuff?

Have you had training? Do you have GN3?
How would you expect to be able to obtain these reading with the fuse removed????????????
 
Nazoom

Until you can get your head around what these tests portray and be taught how to carry them out safely,especially the live testing,removing the main fuse should not be considered

If you have made yourself familiar with the theory and lack the practical experience,it is important that the tests you are carrying out be done firstly under supervision

Only when you are absolutely sure of what it is all about should this be attemted on your own

Because of the nature of the questions, i am sorry but I will be given no advise on how to procede
 
So do i need to re-energise the supply by putting back the supply fuse (100 A fuse ) then turn On the Main switch in the consumer unit. Do i need to do this for Ze, PFC, PSCC, and Zs?

Basically I am asking when Life testing i.e Zs, Ze, PFC, and PSCC do I need to re-energise the supply by putting the 100A fuse back and unlocking the isolater then turn the main switch On at the consumer unit for these test?

Please Help!
 
So do i need to re-energise the supply by putting back the supply fuse (100 A fuse ) then turn On the Main switch in the consumer unit. Do i need to do this for Ze, PFC, PSCC, and Zs?

Basically I am asking when Life testing i.e Zs, Ze, PFC, and PSCC do I need to re-energise the supply by putting the 100A fuse back and unlocking the isolater then turn the main switch On at the consumer unit for these test?

Please Help!
 
Nazoom, I've had a look at your previous posts and I now understand why your asking these questions. Your doing your 2391, I thought you are actually testing in the field. You really need to tell us these things. This time last year you were doing your 2330 level 1. What level have you got to so far? Are you ready to study the 2391 yet? Yes we can help but we won't answer your homework for you. Get your books out, and research the subject and if there are things you are not sure of then ask but please show some effort on your behalf. Please don't take this the wrong way, take it has constructive criticism.
 
I do have GN 3, Wiring Reg, OSG, and some other books but I cant find the answer to this and i have my exam coming soon, I tried looking in these books but i am still unsure about this! My questions are:
Basically I am asking when Life testing i.e Zs, Ze, PFC, and PSCC do I need to re-energise the supply by putting the 100A fuse back and unlocking the isolater then turn the main switch On at the consumer unit for these test? Or Do i leave the 100 A fuse out of its place?

Please Help!
 
Please Help!

How on earth can you be studying at this level without knowing how to answer your own question??

Who is your training provider?


We will help you, but you should be asking yourself what kind of training you have received to need to ask these questions..
 
Last edited:
Yes and no is the answer.

Never heard of life tester either.

Just being truthfull here Nazoom, but if you don't already understand what are very simple tests for any electrician, especially one who is completing the 2391, then when it comes to the written part of you 2391 I think you're going to be stumped.

Not having a go at you, just offering some adice.
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.
I did look in theses books and other books and even searched Utube and I have bought lots of DVDs to help me with this but no good. Also it has been while since I was in the workshop for this course and now i cant find the answer to these questions and they are very important please I don't know who can help me with this any more! My questions are simple and important. My exam date is this January 18th. And I am, freaking out as this will only get worst if I don't find the answers to these questions. So please Help!


Basically I am asking when Life testing i.e Zs, Ze, PFC, and PSCC do I need to re-energise the supply by putting the 100A fuse back and unlocking the isolater then turn the main switch On at the consumer unit for these test?

Much appreciated.
 

Reply to Some questions regarding reinstating the supply fuse for live testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
488
  • Question
UK Strange
i think you're trying to do yourself some damage.... Plugtops are designed to be used with a fuse.... use it Plugging things in when the other...
Replies
10
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top