I am currently training at OLCI. It has been while since my workshop. Now I can't remember what happens in details! but I do remember taking out the 100 A fuse and locking the isolater with a key but I can't remember what happens to the 100 A Fuse in the case of each test: Ze, Zs, PFC, and PSCC?
Ok well I'll be honest and say that I donk think taking out the fuse is a good idea when training students, it leads to confusion. Locking off of the main switch and testing with an approved tester and proving unit will achieve safe isolation.
So breaking down the live tests you have stated..
Ze, PFC & PSCC can be measured with the main switch still locked off, by testing on the supply side. Remember that if it is possible to carry out a test with as little of the installation energised at the time then it is a safer method of testing.
I assume you understand test procedures (removal of main protective conductor etc)..
Zs, however, will need to be measured at the furthest point of each circuit. This is why it is done after Ze, to verify presence of sufficient earthing before energising the system.
So to carry out Zs, isolate each MCB then remove the lock off from the main switch.
Now, one circuit at a time, energise and obtain the Zs readings by measurement. Some of the circuits may not be applicable at this test if Zs has been obtained by calculation.
Hope this made sense, but back to the fuse.. It must be inplace for you to be able to carry out live testing.