I recently carried out a pir on a bungalow that has been modified for a disabled person. There are plenty of faults but the one I am not 100% on how to rectify without to much disruption is as follows.
Next to the bath there is a 230v switched spur that supplies the motorized platform within the bath. This spur is literally about 50mm away from the bath edge! I have coded this as a 1.
Now I have got the remedials I need to work out how best to sort this without disrupting the tiled wall of the wet room. One idea so far is to remove the spur front and replace with an adaptable box and then use plastic conduit up and relocate the spur above 2.25m, extending the cables through the tube. Only thing is I think this may look like an eyesore tbh. The original cables are in plaster behind the walls so I wont be able to pull them up into the space above.
Any other ideas?
I was wondering if you could get an ip65 switched spur (mk masterseal ones for outside) and mount it in place of the original spur front, only thing is the big red book says no 230v switches i zones one or two
Any help would be great as obviously customer wants this done cheap as poss
thanks
I recently carried out a pir on a bungalow that has been modified for a disabled person. There are plenty of faults but the one I am not 100% on how to rectify without to much disruption is as follows.
Next to the bath there is a 230v switched spur that supplies the motorized platform within the bath. This spur is literally about 50mm away from the bath edge! I have coded this as a 1.
Now I have got the remedials I need to work out how best to sort this without disrupting the tiled wall of the wet room. One idea so far is to remove the spur front and replace with an adaptable box and then use plastic conduit up and relocate the spur above 2.25m, extending the cables through the tube. Only thing is I think this may look like an eyesore tbh. The original cables are in plaster behind the walls so I wont be able to pull them up into the space above.
Any other ideas?
I was wondering if you could get an ip65 switched spur (mk masterseal ones for outside) and mount it in place of the original spur front, only thing is the big red book says no 230v switches i zones one or two
Any help would be great as obviously customer wants this done cheap as poss
thanks