Something just doesnt feel right | on ElectriciansForums

Discuss Something just doesnt feel right in the UK Electrical Forum area at ElectriciansForums.net

magnoliafan89

-
Arms
Joined
Feb 12, 2017
Messages
433
Reaction score
636
Location
Hereford
hi guys

Could be wrong but doing a condition report and come across this. Pretty typical for this block of maisonettes to have swa coming from the main building supply into an adaptable box and this set up.

However I've noticed this one has the neutral go straight into the main switch and has a link from the meter....

Could be fine but something is just saying it doesn't feel right.

Is this OK or not??
 

Attachments

  • [ElectriciansForums.net] Something just doesnt feel right
    IMG-20200907-WA0002.jpeg
    66.2 KB · Views: 159
The neutral is usually just a commoning block in the meter but I agree... it just doesn't feel right. I think much of my feels is coming from the quality of the neutral connection in the main switch. That connection to the meter isn't going to be carrying much in the way of current (I believe it's only used in the meter for the voltage sensing and the electronics) but that doesn't preclude the possibility that the connection at the main switch could be bad.

The other thing that peaks my interest is the connection method of the live... looks like a chocblock wrapped in tape. Have only ever used proper uninsulated butt crimps for terminations that large (aside from a couple of large screw junction boxes for cookers/showers) so if it is a chocblock... I think I'd be making a note on the certificate about it.
 
And it looks like someone got to the meter before the Fairies arrived.
Where's the join in the Yellow, presumably a CPC?
Any bonding?

Is that a sub meter or the supplier's?

For those of us with aging eyesight;

[ElectriciansForums.net] Something just doesnt feel right
 
Last edited:
If it's a suppliers meter it's not right, and if it's a checkmeter it's plain daft. The reason the neutral goes through the meter, traditionally, is that the energy charged for is what comes out of the load terminals, because the meter registers the power as the product of the voltage between L & N and the current from supply L to load L. In reality what this translates to is that if the neutral is disconnected from the meter, it doesn't register and the customer gets free electricity. Therefore, the meter's neutral connection must never go through the customer's equipment such that it could be disconnected.

With smart meters with internal motorised switches and batteries, it's possible for the meter to disconnect the customer if current continues to flow through the line terminal in the absence of voltage between line and neutral. But I really can't see why anyone would think this is correct, unless it's the result of previous tampering.
 
If it's a suppliers meter it's not right, and if it's a checkmeter it's plain daft. The reason the neutral goes through the meter, traditionally, is that the energy charged for is what comes out of the load terminals, because the meter registers the power as the product of the voltage between L & N and the current from supply L to load L. In reality what this translates to is that if the neutral is disconnected from the meter, it doesn't register and the customer gets free electricity. Therefore, the meter's neutral connection must never go through the customer's equipment such that it could be disconnected.

With smart meters with internal motorised switches and batteries, it's possible for the meter to disconnect the customer if current continues to flow through the line terminal in the absence of voltage between line and neutral. But I really can't see why anyone would think this is correct, unless it's the result of previous tampering.
Would you code it or make a note??

It comes from a cut out fuse in another part of the building which goes to an old meter this then feeds an mem switchgear from here goes the swa to the adaptable box that you see.
 

Attachments

  • [ElectriciansForums.net] Something just doesnt feel right
    15994880735213908038552265213018.jpg
    72.2 KB · Views: 146
  • [ElectriciansForums.net] Something just doesnt feel right
    15994880973853243207845584981471.jpg
    134.9 KB · Views: 109
  • [ElectriciansForums.net] Something just doesnt feel right
    15994881157515423049106881657341.jpg
    153.3 KB · Views: 105
If it's a suppliers meter it's not right, and if it's a checkmeter it's plain daft. The reason the neutral goes through the meter, traditionally, is that the energy charged for is what comes out of the load terminals, because the meter registers the power as the product of the voltage between L & N and the current from supply L to load L. In reality what this translates to is that if the neutral is disconnected from the meter, it doesn't register and the customer gets free electricity. Therefore, the meter's neutral connection must never go through the customer's equipment such that it could be disconnected.

With smart meters with internal motorised switches and batteries, it's possible for the meter to disconnect the customer if current continues to flow through the line terminal in the absence of voltage between line and neutral. But I really can't see why anyone would think this is correct, unless it's the result of previous tampering.

That's a very good point and one I must admit didn't really cross my mind. Everyday is a school day :)
 
Right, so it's not the supplier's meter. Is the vacant terminal in the meter plugged to a suitable IP rating? Are the tails secure and properly fixed? Looks shonky to me. And, am I seeing things or is that T+E in the meter N and load L terminals? The cables in the series 7 look circular but the others?
 
Certainly a rough install, there are a few suppliers meters wired in a similar '3 wire' fashion in the local area. Often seen when the meter has been moved from high level down to low level as they see it as dangerous if the user has to climb on something to reach a key meter. The neutral block would be sealed though and the unused N hole plugged...
 
If I read this right, the SWA is already metered at the main cut-out? And maybe that meter local to the DB is redundant so it has been bypassed, maybe. Think I would C2 exposed live terminals at that meter, unless there is a cover for it? Maybe a note on the condition of the suppliers equipment/meter. I think those meters have an internal fuse if that went it could be difficult to remedy/find.
[automerge]1599502200[/automerge]
And what about the fly-lead as well?
 
Last edited:
If I read this right, the SWA is already metered at the main cut-out? And maybe that meter local to the DB is redundant so it has been bypassed, maybe. Think I would C2 exposed live terminals at that meter, unless there is a cover for it? Maybe a note on the condition of the suppliers equipment/meter. I think those meters have an internal fuse if that went it could be difficult to remedy/find.
[automerge]1599502200[/automerge]
And what about the fly-lead as well?
I took the cover off. That meter is still in use.
Don't fret though I isolated the supply to everything in the flat from the original MEM switch in the main building and proved dead.

Fly lead???
 

Reply to Something just doesnt feel right in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
816
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top