spare cores when using armoured help | on ElectriciansForums
Discuss spare cores when using armoured help in the Electrician Talk | All Countries area at ElectriciansForums.net
stumas
a panel which is fed by 2x 15o mm 4core armouds which is using the amoring for the eath
has the 2 neutrall conducters tapped up inside the panel as no nuatral is required is thi ok or should they be connected to earth is there a regulation about spare cores or any recomendations help please
I assume the armour is used as the earth,? no problem with insulating them and leaving them in the board, or your could sleeve them and use as cpc.
Reg 537.2.1.4. You muist ground spare conductors in any cable to reduce the risk of inductive voltage.
537.2.1.4 Where necessary, suitable means shall be provided for the discharge of stored electrical energy
At least thats what my electronic BRB version says.....
Reply to spare cores when using armoured help in the Electrician Talk | All Countries area at ElectriciansForums.net
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...