So am i correct than reg 443.4 means unless we provide a risk assesment that states why we are not using a spd in consumer unit changes then we must fit one??
 
The risk assessment according to 443.5 is required if protection against transient over voltage is even required for electrical installations except single dwelling units.
If not performed then the installation shall be provided with transient over voltage protection.
Regulation 443.1.1 states that this section does not specify requirements for protection against transient overvoltages due to direct lighting strokes on a structure.
Again I do not see where a type 1 is required if no LPZ is present as figure 534.1 indicates the LPZ concept

It’s definitely one for debate/guidance/clarity?
I’m sure I’ll get there in the endo_O

Having just read it all I agree with you. No lightning protection installed then no Type 1 required.
 
How do you decide if lightning protection is even required?
I know a risk assessment is required and is under a different British standard, but how do you evaluate if an LPZ system should be considered?
 
[ElectriciansForums.net] Spd & 18th..............,,,,,,

we are been round that above ,about spd ,fit or no fit that is the question .;)
 
How do you decide if lightning protection is even required?
I know a risk assessment is required and is under a different British standard, but how do you evaluate if an LPZ system should be considered?

That would be the responsibility of the building owner to sort. We are working with a lightning company at the moment and I asked a similar question a few weeks back and they use a software package that does the RA for them. He said it is almost always required and it would literally need to be an emtpy shell for the RA to state no protection required.
 
Manufacturers guides really do not help.

To be fair once you spend a bit of time reading the section on SPDs it is quite clear.

I should probably pay more attention / show more interest to the 18th.

My 18th isn’t booked until mid December & As changes don’t take effect untill Jan 1st I really have no interest at the moment.
 

Reply to Spd & 18th..............,,,,,, in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You'd have to be mindful of SPD conductor lengths doing it that way. I think Matt:E make a single board with Type A RCBO, openPEN detection and...
Replies
1
Views
1K
If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
318

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top