just been handed this to fit to a TPN DB,have you seen anything so ridiculous,it’s a SPD, those cables are so short,
 

Attachments

  • [ElectriciansForums.net] Spd on Eaton Tpn
    ABCF42A3-7DDD-4881-8F67-BD5D3DFA518F.jpeg
    94.2 KB · Views: 45
I think they are supposed to be mounted on the side of the DB, closest to the main switch, via a high current breaker (32A or more D-curve, etc) or in some cases just joining blocks. Not sure if there are any punch-out holes or you are expected to drill something.

The short cables are needed to keep the inductance down as lighting surges are only tens of microseconds long and so L usually dominates of R in most cases. A quick look in the 18th regs has max 1m but preferred less than 0.5m total wiring, so 2 * 25cm to the SPD.

Same reason for going for a MCB with a high magnetic trip point - less of a coil for that so lower series inductance.
 
just been handed this to fit to a TPN DB,have you seen anything so ridiculous,it’s a SPD, those cables are so short,

Yes, the cables must be kept as short as possible, if you make them much longer than that then the SPD won't work properly.

Those cables will be exactly the right length to fit the device where the manufacturer specifies that it goes.
 
Cheers,this is an add on to existing Tpn,where it’s impossible to mount with those connections,to the side of the TPN.
Bearing in mind the max distances,possible to connect @ 1m max with 16mm ,mcb rated @ 63 amp.
 
Cheers,this is an add on to existing Tpn,where it’s impossible to mount with those connections,to the side of the TPN.
Bearing in mind the max distances,possible to connect @ 1m max with 16mm ,mcb rated @ 63 amp.

You'll need to speak to Eaton technical support, only they can tell you what is acceptable for their SPD.
 

Reply to Spd on Eaton Tpn in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It looked like the live connection side ( internally) burned against the neutral of the main switch
2
Replies
23
Views
1K
  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top