Spd specifications | on ElectriciansForums

Discuss Spd specifications in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Joined
Aug 2, 2013
Messages
1,912
Reaction score
880
Location
leicester
Iv been tasked with upgrading a 16th edition board with a schneider 6 + 8 way acti9 board with spd protection.

SPD was specified for me so I dont have to perform the calculation, however, I am stuck with the specifics of the devices themselves.

Firstly, can the device hang of the back of an rcbo or is rcd protection not a requirement for them? Is mcb for overcurrent protection sufficient?

I have ascertained the SPD will be a type 2 with a replaceable cartridge, however there are so many other figures that are listed on Schneider website and such there are numerous different type 2 devices. I'm a little baffled.

Do I need to factor into account Imax? Limp?

Am I over complicating it?
 
The SPD should be before any RCD/RCBO (except sometimes in it is a delay RCD for TT incomer). RCD don't enjoy carrying the surge current and the RCD impedance means parallel circuits (off the supply) have poor protection.

All SPD need some form of OCPD but the device specks should tell you want. Often it is a fuse in the 125-315A sort or range and then the incoming DNO fuse is adequate. Others require a MCB for it, but that should be low inductance so something like a 32A D-curve is probably a good choice. Again, check the manufacturer's recommendation.

So generally the SPD is directly off the busbar or a MCB dedicated to it.

The actual surge handling is usually a minor issue unless you have a type-1 for a building with lightning protection and then you have a handful of categories of protection level that give acceptable probabilities that the SPD is big enough.
 

Reply to Spd specifications in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
955
  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top