Iv been tasked with upgrading a 16th edition board with a schneider 6 + 8 way acti9 board with spd protection.

SPD was specified for me so I dont have to perform the calculation, however, I am stuck with the specifics of the devices themselves.

Firstly, can the device hang of the back of an rcbo or is rcd protection not a requirement for them? Is mcb for overcurrent protection sufficient?

I have ascertained the SPD will be a type 2 with a replaceable cartridge, however there are so many other figures that are listed on Schneider website and such there are numerous different type 2 devices. I'm a little baffled.

Do I need to factor into account Imax? Limp?

Am I over complicating it?
 
The SPD should be before any RCD/RCBO (except sometimes in it is a delay RCD for TT incomer). RCD don't enjoy carrying the surge current and the RCD impedance means parallel circuits (off the supply) have poor protection.

All SPD need some form of OCPD but the device specks should tell you want. Often it is a fuse in the 125-315A sort or range and then the incoming DNO fuse is adequate. Others require a MCB for it, but that should be low inductance so something like a 32A D-curve is probably a good choice. Again, check the manufacturer's recommendation.

So generally the SPD is directly off the busbar or a MCB dedicated to it.

The actual surge handling is usually a minor issue unless you have a type-1 for a building with lightning protection and then you have a handful of categories of protection level that give acceptable probabilities that the SPD is big enough.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
-
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Spd specifications
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
gazdkw82,
Last reply from
gazdkw82,
Replies
2
Views
1,579

Advert

Back
Top