Evening , been to look a job this evening for an additional socket in kitchen . When checking out board an spd has been fitted but the supply is is coming off an 20amp mcb that looks like it is feeding a small radial circuit . Is this a total no no . I think it is and I have explained to customer that he needs it changed etc. I can see why it has been down as it is an old board with GE ep61 mcb which are difficult to get hold off . Just wondered what people thought are on this
 
A stand-alone or dedicated circuit breaker for surge protector performs the following functions:

  • Allows power to the surge protector to be removed without interrupting power to other loads.
  • If a component fails inside the protector, only the circuit breaker will trip, and the power of any other load will not be disturbed.
So if the client is happy with the above restrictions then I don't think it is a problem. The MCB is only to protect the electronics of the SPD is my understanding but stand to be corrected.

The other consideration is that it is not advised to do Insulation Resistance testing on installed SPDs (NICEIC Guidance). I guess not being on its own breaker could mean the SPD is included in a IR test if it was not noticed that it is supplied from the circuit supplying the radial.

Guidance here

Regulation 643.3.2 permits the following actions when items of equipment such as SPDs are likely to influence the results of an insulation resistance test or may suffer damage as a result of an applied test voltage of 500 V DC:

● Wherever possible the equipment should be disconnected prior to carrying out the test. In many cases, this is a practical option as the SPD will be installed in parallel and a means of isolation should have been provided to facilitate inspection and replacement of either component parts or the device. This is not such a practical proposition where an installation contains multiple SPDs incorporated into socket-outlets, for example. Once testing is complete it is essential that all disconnected SPDs are re-connected.


The other thing of course is, is it installed to manufacturers instructions? MCB is of the correct rating for the SPD etc
 
A stand-alone or dedicated circuit breaker for surge protector performs the following functions:

  • Allows power to the surge protector to be removed without interrupting power to other loads.
  • If a component fails inside the protector, only the circuit breaker will trip, and the power of any other load will not be disturbed.
So if the client is happy with the above restrictions then I don't think it is a problem. The MCB is only to protect the electronics of the SPD is my understanding but stand to be corrected.

The other consideration is that it is not advised to do Insulation Resistance testing on installed SPDs (NICEIC Guidance). I guess not being on its own breaker could mean the SPD is included in a IR test if it was not noticed that it is supplied from the circuit supplying the radial.

Guidance here

Regulation 643.3.2 permits the following actions when items of equipment such as SPDs are likely to influence the results of an insulation resistance test or may suffer damage as a result of an applied test voltage of 500 V DC:

● Wherever possible the equipment should be disconnected prior to carrying out the test. In many cases, this is a practical option as the SPD will be installed in parallel and a means of isolation should have been provided to facilitate inspection and replacement of either component parts or the device. This is not such a practical proposition where an installation contains multiple SPDs incorporated into socket-outlets, for example. Once testing is complete it is essential that all disconnected SPDs are re-connected.


The other thing of course is, is it installed to manufacturers instructions? MCB is of the correct rating for the SPD etc
Some Spd,s have internal protection and therefore doesn't have an external Mcb.
 

Reply to Spd supplied of exsisting mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
  • Question
Sorry for the reply delay! No, there is nothing of value connected in the barn, just a few socket outlets and lights etc. I think due to the...
Replies
3
Views
3K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
1K
davesparks
D
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks