Morning,

I've got a job on what was once a dairy farm, it hasn't been used as such for many years, it has a 3ph supply to the house from which the single pahse db in the house is fed with a 3ph supply going out to the old barns and milking parlour.
It appears that the earthing arrangement for the whole installation is a TNCS, I can't find any trace of a TT installation for the out buildings.

I have rewired the house, no problems but now the owner wants the installation in the out buildings upgrading, it has an old board with BS 3036 fuses which supplys mostly lighting and some sockets, the owner wants it all re-wiring new lighting and some additional sockets for general use and light commercial use(one building will be a wood shop for his own use) the question is should it be classed as a special location still or can I treat it as you would for normal outbuildings and what are your thoughts on RCD protection?

TIA
 
You can only treat the new installation at face value and your design criteria is for a small commercial outlet and therefore that is what you design for. So a buildings former use is really irrelevant

That is one building you mention, are there any plans for the others.

As for RCD, personally I would not be going down that road for this type of installation. But to be honest I would like to see a scope of requirements before I commented too much on that
 
Last edited:
I would say that as long as these building upgrades are not being used for livestock of any kind, it's not a ''Special Location'' and the PME supply is suitable for these buildings new useage, such as a personal wood working shop!!

If any of these outbuildings was going to be used again as a milking palour, then you would need to leave the PME behind and TT the milking parlour (or any of the outbuildings if being used for livestock)
 

Reply to Special Location or Not?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
318
Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
362
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
379
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
870
  • Question
Thanks for that advice. I don't know the MV capacity locally, though there are lots of wind farms several miles away so generation is not such a...
Replies
2
Views
898

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks