Can anyone tell me what table to use for CCA of split concentric in BS 7671?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Split concentric cable in the UK Electrical Forum area at ElectriciansForums.net
It definently does exist not sure why they don't show it on that sheetI've always thought 10mm2 SC didn't exist. None of my wholesalers kept it in stock.
Doncaster have info on their site
Cheers mate!Doncaster cable data sheet has it:
Values in the data sheet are only marginally higher than 70C PVC cables (e.g. Table 4D2A column 8), so you can probably use those tables if you are using it in other installation methods.
Reply to Split concentric cable in the UK Electrical Forum area at ElectriciansForums.net