I think √2 comes in to it somewhere doesn’t it Dave?

I don’t think we’re wrong, but you never know.

240V RMS = 339.41V peak→base line.

Its called the crest factor, and it takes you from peak to RMS, although under certain condtions(Fault) the crest value can be greater.

Stop playing the smart arse. Learn about transformer phase and vector diagrams.

Okay, if the vectors are in phase, or 180 Degrees apart you get the same answer, though from reading J & P transformer book and other publications they state 180 degree, some were 90 degree.


Cheers
 
FFs its centre tapped there would be a sine wave above and below the base line

take 2 comming in a mo

 
Last edited by a moderator:
Take three

For the "in phase vectors" to add we need a series connection within the Tx, this isnt the case, and it the vectors were 180 degree apart and wired in series they would subtract.

The Tx is center tapped, extract.

Center-tap transformer. The tapping point is in the exact center of the secondary winding providing a common connection for two equal but opposite secondary voltages. With the center-tap grounded, the output
V[SUB]A[/SUB]
will be positive in nature with respect to the ground, while the voltage at the other secondary,
V[SUB]B[/SUB]
will be negative and opposite in nature, that is they are 180[SUP]o[/SUP] electrical degrees out-of-phase with each other.

Now VA= NA/NP * VP
VB= NB/NP* VP

230 at 0 Degrees plus 230 at 180 degree = 460 Volts
 
Take four

If we have a winding that delivers 480 volts, we earth one end(0 V and reference) and tap 1/4, 1/2 and end we would measure 120 v, 240 v and 480 v all in phase from that reference.

If we center tap the winding and earth(0 v and reference) what we would see is at the end of one winding 240 + and the other end 240 -.

So the two phases from the center tap reference are 180 degrees apart.

Cheers
 
Your just not getting this are you. Convention with transformers is governed by angular orientation of the windings not the output waveform.

I’m not continuing this further on here due to constraints imposed on me by the moderators.

some were 90 degree.

90° phase displacement. Explain for the other members.
 
Last edited by a moderator:
This is quite simple, its classed as a single phase three wire system. In effect two phases 180 degree apart, the neutral point being at the center between the two phases.

They cant be in phase, draw out two vectors with the same direction and magnitude.

Cheers
Agree, the wave forms are 180 degree apart.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Split phase
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
46

Thread Tags

Advert

Thread statistics

Created
jimmer,
Last reply from
Leyland30,
Replies
46
Views
10,838

Advert

Back
Top