by calculation, you are correct, but due to parallel paths (water pipes etc.) to earth, the Zs can be lower than calculated. this is most noticeable in TT systems where the resistance to earth through services is less than the resistance through the earth rod.

This is why the Zs-Ze = (R1+R2) formula should never be used as it makes no allowance for the parallel paths that exist in all but the most basic of 'all-insulated' installations.
 
i,m back ther tomorrow so will start taking my own readings, i was going off the existing readings today for an overview of the existing installation
 
i think i need to review my test procedures , i have always measured Ze at the supply incomer, then R1 + R2 and added them together obviously not allowing for parallel earths, you learn something new every day on here and i dont mind admitting it
 
i always measure Zs unless by doing so i might create danger for myself or others. to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.
 
i think i need to review my test procedures , i have always measured Ze at the supply incomer, then R1 + R2 and added them together obviously not allowing for parallel earths, you learn something new every day on here and i dont mind admitting it

Your procedure still complies, measurement or calculation.

I'm a confirmed measurer!
 
i always measure Zs unless by doing so i might create danger for myself or others. to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.

I will try that tomorrow as the hotel is vacant week days and see what results i get , many thanks Telectrix
 
Hi guys ... just to keep you updated ... i havent been back to the job yet but should be back there monday so will let you know what i find
Andy
 
to give an idea of the effect of parallel paths, measure Ze as normal with the main earth dissed. then measure again with it connected. you should find the 2nd reading is lower.

Shouldn't this be done anyway, as your as part of your PFC test (PEFC) ?
 
Last edited:

Reply to Spot the mistakes - Billy Bulls**t circuit sheets i think in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top