Domestic Scenario
There is an existing 32A ring circuit protected by BS60898 MCB. The wiring is flush <50mm deep.
Upgrading a storage heater I need to add a FCU for the boost funtion on the storage heater. The wiring is surface for the FCU.
A colleague says it is ok to come directly from the top of the 32A fuse for a single spur (but not from anywhere else, ie: JB on one leg of the ring circuit as it leaves the CU on the surface).
My problem is how can this comply with regs.
Whilst I can see the cable will not be overloaded due to the fuse size in the FCU, Is it classed as 1 circuit or 2 circuits.
If it's 1, then the circuit has been altered and needs to be brought up to current standards, RCD protection to the circuit.
or
If it's 2, then the circuits have been bunched which is not allowed.
Cheers